I am looking for another opinion on whether the Fire Department Connections
need to be "interconnected" when a large building is supplied by more than
one underground service/riser.  The case I have in mind is a large warehouse
(200,000 sq ft) with risers at opposite ends as was commonly done in the
past.  Is there a code requirement or good practice recommendation?

NFPA 13-2010 paragraph 8.17.2.4.5 states "*Where a fire department
connection services only a portion of a building, a sign shall be attached
indicating the portions of the building served*."  Is section intended to
apply to a partially sprinklered buildings to advise that the entire
building is not protected?  Or is it intended to permit multiple FDCs as
long as you clearly indicated which portion of the building it protects?

I am aware that NFPA 14 paragraph 7.5.1 states "*Where two or more
standpipes are installed in the same building or section of building, they
shall be interconnected*."  But for this specific case there would be no
standpipes.

Thanks in advance,
Mark Gouveia
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to