I'll bet the site system on such a large building also serves hydrants. Mark - I don't think there's any requirement for interconnection. 13 says that a "system" requires an FDC, not a "building". I have worked with fire departments to interconnect multiple FDC's on special consideration sites, and have interconnected multiple interior systems to a single FDC, all in the name of making it easier/safer for the FD to step down and plug in with as little drama and confusion as possible. But I'm 99% sure the standard is mute regarding interconnection ...
Steve Leyton Protection Design & Consulting San Diego, CA -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of [email protected] Sent: Friday, July 08, 2011 10:34 AM To: [email protected] Subject: RE: Single Building - Multiple Services and FDCs Why not put the FDC @ the fire service vault near the street and connection to the municipal main?Interconnecting could get costly and this would serve the same purpose. Lamar Vaughn,SET On Fri, Jul 8, 2011 at 1:23 PM, Mark Gouveia wrote: > I am looking for another opinion on whether the Fire Department > Connections > need to be "interconnected" when a large building is supplied by more > than > one underground service/riser. The case I have in mind is a large > warehouse > (200,000 sq ft) with risers at opposite ends as was commonly done in > the > past. Is there a code requirement or good practice recommendation? > > NFPA 13-2010 paragraph 8.17.2.4.5 states "*Where a fire department > connection services only a portion of a building, a sign shall be > attached > indicating the portions of the building served*." Is section intended > to > apply to a partially sprinklered buildings to advise that the entire > building is not protected? Or is it intended to permit multiple FDCs > as > long as you clearly indicated which portion of the building it > protects? > > I am aware that NFPA 14 paragraph 7.5.1 states "*Where two or more > standpipes are installed in the same building or section of building, > they > shall be interconnected*." But for this specific case there would be > no > standpipes. > > Thanks in advance, > Mark Gouveia > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email > to:[email protected] > (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)