Mark,
It's not mandatory to interconnect the different fire dept. connections.
However if you don't interconnect them it is very difficult for the fire
dept. to know the building area that the specific fire dept. connection
serves, especially in a fire condition where things are happening
quickly.
Paragraph 8.17.2.4.5 refers to a partially sprinklered building so the
fire department is aware of that and they can fight the fire
accordingly. 
If you don't want to interconnect the fire dept. connections the best
thing to do is ask the AHJ and get their input.


George Macris,Plans Examiner/Fire Prevention Officer
Markham Fire & Emergency Services
101 Town Centre Boulevard
Markham, Ontario L3R 9W3
(905) 477-7000 ext. 4240 or 2210 Fax (905) 479-7770
[email protected]  www.markham.ca




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Mark
Gouveia
Sent: Friday, July 08, 2011 1:23 PM
To: [email protected]
Subject: Single Building - Multiple Services and FDCs

I am looking for another opinion on whether the Fire Department
Connections
need to be "interconnected" when a large building is supplied by more
than
one underground service/riser.  The case I have in mind is a large
warehouse
(200,000 sq ft) with risers at opposite ends as was commonly done in the
past.  Is there a code requirement or good practice recommendation?

NFPA 13-2010 paragraph 8.17.2.4.5 states "*Where a fire department
connection services only a portion of a building, a sign shall be
attached
indicating the portions of the building served*."  Is section intended
to
apply to a partially sprinklered buildings to advise that the entire
building is not protected?  Or is it intended to permit multiple FDCs as
long as you clearly indicated which portion of the building it protects?

I am aware that NFPA 14 paragraph 7.5.1 states "*Where two or more
standpipes are installed in the same building or section of building,
they
shall be interconnected*."  But for this specific case there would be no
standpipes.

Thanks in advance,
Mark Gouveia
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
**************************************************************************************************

This e-mail contains information that may be privileged and/or confidential.  
If you are 
not the intended recipient, any disclosure, distribution, copying or other use 
of this 
e-mail or the information contained herein or attached hereto is strictly 
prohibited and 
may be unlawful. If you have received this e-mail in error, please notify this 
sender 
immediately and delete this e-mail without reading, printing, copying or 
forwarding it to 
anyone. Thank you for your co-operation.

**************************************************************************************************

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to