How about a 2x4 or drywall ceiling installed at top of the existing walls. The 
fencing already provides security. Be a heckuva lot cheaper, not that cost 
would be the overriding criteria....unless the project is over and there's no 
money left except the maintenance budget.


George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Tuesday, July 26, 2011 11:20 AM
To: [email protected]
Subject: RE: Concealed Space?

Not a concealed space by any stretch.

If the top of the cell is open to the space above the ceiling how are they 
heating and cooling the cell?

Above the cell fence at the top they should extend the wall up to the deck with 
studs and sheetrock,  just for separation and environmental control.  I can't 
see how they would control heat and cooling in the cell without doing that.  If 
they did that then the two heads you described should be acceptable.  

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Tuesday, July 26, 2011 9:46 AM
To: [email protected]
Subject: Concealed Space?

Okay here is the situation. I have a Medical/Dental Facility which is part 
of a prison complex. The building is a noncombustible Butler type building 
approx. 6,200 sq. ft. in area. Ceilings are a combination of suspended 
ceiling tile and drywall. Walls are metal studs and drywall. Pretty 
straightforward so far. However they have a Detainee Holding Cell which is 
approx. 175 sq. ft. in area with a mesh type ceiling (almost like heavy 
duty chain link fence) above. From inside the cell you can look up and see 
the roof deck above. The walls around the cell are concrete block and only 
extend about 6" above the ceiling area of the adjacent rooms. This is a 
holding cell only, no bed, etc. Inmates wait in this cell before being 
removed for examination. Sprinkler protection is installed throughout the 
entire drop ceiling area. No sprinkler protection at the roof deck above 
except for two heads over the cell. Heads are about 5'-6' above cell.  Is 
this acceptable? Is this space still considered a noncombustible concealed 
space not requiring sprinkler protection throughout? My thinking is that 
for this to be acceptable the walls around the cell should extend to the 
roof deck. 

Matt
Matthew Drewello, P.E. l FLUOR l Senior Design Engineer - Fire Protection 
l [email protected] l O +864.517.1814 l www.fluor.com
------------------------------------------------------------
The information transmitted is intended only for the person 
or entity to which it is addressed and may contain 
proprietary, business-confidential and/or privileged material.  
If you are not the intended recipient of this message you are 
hereby notified that any use, review, retransmission, dissemination, 
distribution, reproduction or any action taken in reliance upon 
this message is prohibited. If you received this in error, please 
contact the sender and delete the material from any computer.  

Any views expressed in this message are those of the individual 
sender and may not necessarily reflect the views of the company.  
------------------------------------------------------------
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to