Could you apply NFPA 13 (2002) section 8.14.1.5? (or the newer equivalent)

At 09:45 AM 7/26/2011, you wrote:
>Okay here is the situation. I have a Medical/Dental Facility which is part 
>of a prison complex. The building is a noncombustible Butler type building 
>approx. 6,200 sq. ft. in area. Ceilings are a combination of suspended 
>ceiling tile and drywall. Walls are metal studs and drywall. Pretty 
>straightforward so far. However they have a Detainee Holding Cell which is 
>approx. 175 sq. ft. in area with a mesh type ceiling (almost like heavy 
>duty chain link fence) above. From inside the cell you can look up and see 
>the roof deck above. The walls around the cell are concrete block and only 
>extend about 6" above the ceiling area of the adjacent rooms. This is a 
>holding cell only, no bed, etc. Inmates wait in this cell before being 
>removed for examination. Sprinkler protection is installed throughout the 
>entire drop ceiling area. No sprinkler protection at the roof deck above 
>except for two heads over the cell. Heads are about 5'-6' above cell.  Is 
>this acceptable? Is this space still considered a noncombustible concealed 
>space not requiring sprinkler protection throughout? My thinking is that 
>for this to be acceptable the walls around the cell should extend to the 
>roof deck. 
>
>Matt
>Matthew Drewello, P.E. l FLUOR l Senior Design Engineer - Fire Protection 
>l [email protected] l O +864.517.1814 l www.fluor.com
>------------------------------------------------------------
>The information transmitted is intended only for the person 
>or entity to which it is addressed and may contain 
>proprietary, business-confidential and/or privileged material.  
>If you are not the intended recipient of this message you are 
>hereby notified that any use, review, retransmission, dissemination, 
>distribution, reproduction or any action taken in reliance upon 
>this message is prohibited. If you received this in error, please 
>contact the sender and delete the material from any computer.  
>
>Any views expressed in this message are those of the individual 
>sender and may not necessarily reflect the views of the company.  
>------------------------------------------------------------
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to