Continuing prior posting, I do not recall ever looking for a pressure loss 
through a hydrant.  The data may be available from the mfr, but if not, you may 
have to make an estimate based on the design of the hydrant valve.  At the 
least, it will be a sharp 90 and something like a globe valve.  My Crane pipe 
and fittings book puts a nominal 6" (my estimate of a 5-1/4 inch typical 
Mueller hydrant) globe valve at about 160' of pipe.  Add your elbow and tee 
plus lead-in piping and run a Hazen Williams calc for the loss.

Dave 

David A. de Vries, P.E., CSP 
Firetech Engineering Incorporated 