Not all flexible sprinkler head pipe systems are listed for dry system use, but those that are can be from what I understand. I believe this scenario is the only reason they're even listed for use in a dry system. You'll need to face your branch outlets up obviously to get the return bend effect. I believe Viking's Flex Head system is listed, but you should check, there are or were 2-3 systems and most people call them all flex heads so you need to be sure the actual system you're using is listed. Mike Morey, SET, CFPS Sprinkler Designer BMW Constructors, Inc. O: 317.651.0596 | C: 317.439.2695 www.bmwc.com
________________________________ From: [email protected] on behalf of Greg McGahan Sent: Thu 8/11/2011 9:20 AM To: [email protected] Subject: Flex heads in lieu of return bends If this has been discussed previously I could not find it on the forum or in the informal interps.. Can a flex head be installed in such a manner to replace a return bend in accordance with 7.2.2 (returns bends feeding heads in which both are in a heated space on a dry system) Thanks, Greg -- Greg McGahan Living Water Fire Protection, LLC <http://www.livingwaterfp.com <http://www.livingwaterfp.com/> > 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 fax 850-937-1852 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)