the advantage is only that all of the other heads on the project are on flex
drops and there are 4 pendents on a dry system and it would be much simpler
to install them all and keep moving. It is not a big deal either way to us.
Greg

On Thu, Aug 11, 2011 at 11:55 AM, Ron Greenman <[email protected]>wrote:

> You'd need to make sure your bend had the correct radius also so I see no
> advantage to it.
>
> On Thu, Aug 11, 2011 at 8:35 AM, George Church <[email protected]
> >wrote:
>
> > I'd agree that a flexible drop listed for dry systems, or not limited in
> > its listing to wet, installed in a manner that goes up off the line and
> then
> > down to the sprinkler, will fulfill the intent of the code both in
> language,
> > intent and actually DO what it is supposed to do.
> >
> > IF I was entitled to an opinion like Bill and several others, that's what
> > it'd be.
> >
> >
> > George L.  Church, Jr., CET
> > Rowe Sprinkler Systems, Inc.
> > PO Box 407, Middleburg, PA 17842
> > 877-324-ROWE       570-837-6335 fax
> > [email protected]
> >
> >
> >
> > -----Original Message-----
> > From: [email protected] [mailto:
> > [email protected]] On Behalf Of Morey, Mike
> > Sent: Thursday, August 11, 2011 9:34 AM
> > To: [email protected]
> > Subject: RE: Flex heads in lieu of return bends
> >
> > Not all flexible sprinkler head pipe systems are listed for dry system
> use,
> > but those that are can be from what I understand.  I believe this
> scenario
> > is the only reason they're even listed for use in a dry system.  You'll
> need
> > to face your branch outlets up obviously to get the return bend effect.
>  I
> > believe Viking's Flex Head system is listed, but you should check, there
> are
> > or were 2-3 systems and most people call them all flex heads so you need
> to
> > be sure the actual system you're using is listed.
> >
> > Mike Morey, SET, CFPS
> > Sprinkler Designer
> > BMW Constructors, Inc.
> > O: 317.651.0596 | C: 317.439.2695
> > www.bmwc.com
> >
> > ________________________________
> >
> > From: [email protected] on behalf of Greg McGahan
> > Sent: Thu 8/11/2011 9:20 AM
> > To: [email protected]
> > Subject: Flex heads in lieu of return bends
> >
> >
> >
> > If this has been discussed previously I could not find it on the forum or
> > in the informal interps..
> >
> > Can a flex head be installed in such a manner to replace a return bend in
> > accordance with 7.2.2 (returns bends feeding heads in which both are in a
> > heated space on a dry system)
> >
> > Thanks,
> > Greg
> >
> > --
> > Greg McGahan
> > Living Water Fire Protection, LLC <http://www.livingwaterfp.com <
> > http://www.livingwaterfp.com/> >
> > 1160 McKenzie Road
> > Cantonment, FL 32533
> > 850-937-1850
> > fax 850-937-1852
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email
> to:[email protected]
> > (Put the word unsubscribe in the subject field)
> >
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email
> to:[email protected]
> > (Put the word unsubscribe in the subject field)
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email
> to:[email protected]
> > (Put the word unsubscribe in the subject field)
> >
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
>
> [email protected]
>
> http://www.bates.ctc.edu/fireprotection/
>
> 253.680.7346
> 253.576.9700 (cell)
>
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC
>
> They are happy men whose natures sort with their vocations. -Francis Bacon,
> essayist, philosopher, and statesman (1561-1626)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to