I'd agree that a flexible drop listed for dry systems, or not limited in its 
listing to wet, installed in a manner that goes up off the line and then down 
to the sprinkler, will fulfill the intent of the code both in language, intent 
and actually DO what it is supposed to do.

IF I was entitled to an opinion like Bill and several others, that's what it'd 
be.


George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Morey, Mike
Sent: Thursday, August 11, 2011 9:34 AM
To: [email protected]
Subject: RE: Flex heads in lieu of return bends

Not all flexible sprinkler head pipe systems are listed for dry system use, but 
those that are can be from what I understand.  I believe this scenario is the 
only reason they're even listed for use in a dry system.  You'll need to face 
your branch outlets up obviously to get the return bend effect.  I believe 
Viking's Flex Head system is listed, but you should check, there are or were 
2-3 systems and most people call them all flex heads so you need to be sure the 
actual system you're using is listed.
 
Mike Morey, SET, CFPS
Sprinkler Designer
BMW Constructors, Inc.
O: 317.651.0596 | C: 317.439.2695
www.bmwc.com

________________________________

From: [email protected] on behalf of Greg McGahan
Sent: Thu 8/11/2011 9:20 AM
To: [email protected]
Subject: Flex heads in lieu of return bends



If this has been discussed previously I could not find it on the forum or in 
the informal interps..

Can a flex head be installed in such a manner to replace a return bend in 
accordance with 7.2.2 (returns bends feeding heads in which both are in a 
heated space on a dry system)

Thanks,
Greg

--
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com 
<http://www.livingwaterfp.com/> >
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to