A prime example of this would be an office building that by code doesn't 
require sprinklers but the owner decides to install them anyway.  If he does 
then the installation must conform to the applicable Code and Standard.

This is not really that complicated.


Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Thursday, August 11, 2011 3:04 PM
To: [email protected]
Subject: non-required systems

The exception in section 901.2 of the IBC (2003) states: "Exception: Any fire 
protection system or portion thereof not required by this code shall be 
permitted to be installed for partial or complete protection provided that such 
system meets the requirements of this code."  Does this mean that an 
Architect/Owner can pick and chose what the wants to protect if the system is 
not required? Anybody dealt with this from a liability standpoint?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to