Yes we meet all the criteria but unfortunately this AHJ follows 2007.  I will 
tell the GC to add some insulation to these also.
Thanks everybody!

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Sprinkler 
Academy - C Bilbo
Sent: Friday, October 21, 2011 8:27 AM
To: FORUM
Subject: RE: Mansards - NFPA 13


We put allowances in the 2010 edition.  But you gotta meet the four criteria 
found after the following paragraph.
 
Let us know if your mansard meets the requirements.
 
 
 
8.15.1.2.18 Sprinklers shall be permitted to be omitted from within combustible 
soffits, eaves, overhangs, and decorative frame elements that are constructed 
in accordance with
8.15.1.2.18.1 through 8.15.1.2.18.4.
 
 




It should be recognized that the above is my opinion as a member of the NFPA, 
and has not been processed as a formal interpretation in accordance with the 
NFPA Regulations Governing Committee Projects and should therefore not be 
considered, nor relied upon, as the official position of the the AFSA, NFSA, 
NFPA, nor any of their technical committees.

Sincerely,


Cecil Bilbo
Academy of Fire Sprinkler Technology
Champaign, IL
217.607.0325
www.sprinkleracademy.com<http://www.sprinkleracademy.com>

[email protected]<mailto:[email protected]>



OUR STUDENTS SAVE LIVES!!



----------------------------------------
> Date: Fri, 21 Oct 2011 08:32:43 -0400
> To: [email protected]
> From: [email protected]
> Subject: Re: Mansards - NFPA 13
>
> I have had them fill the mansards with insulation because they can present an 
> exposure problem. Have him cover all of the spaces or use fire treated 
> lumber. There is nothing in NFPA 13 which allows for omission of small spaces.
>
>
> At 06:59 AM 10/21/2011, you wrote:
> >Is there anything in NFPA that allows omission of sprinklers in combustible 
> >mansards or similar features built on the outside of a building? I have a 
> >project in which these decorative features are being built on the roof to 
> >hide mechanicals and at the top floor along the outside wall to give a 
> >"castle tower" effect. No mechanicals inside, just dead space separated from 
> >the main building by either a wall or a roof. I have told the GC to fill 
> >them with non-combustible insulation but there is a cornice that that is 
> >2ftx2ft (actually ½ because it looks like a triangle) that will be framed 
> >with 2X6 16in OC that will look like a ledge for the windows. He is asking 
> >if it also needs insulation. My gut feeling is no because it is such a small 
> >area.
> >
> >Thanks,
> >
> >
> >
> >Dewayne Martinez
> >
> >Design Build Fire Protection
> >
> >262-781-7900 (w)
> >
> >262-781-8401 (f)
> >
> >414-349-0468 (cell)
> >
> >
> >
> >-------------- next part -------------- An HTML attachment was 
> >scrubbed...
> >URL: 
> ><http://fireball.firesprinkler.org/mailman/private/sprinklerforum/att
> >achments/20111021/831e38d2/attachment.html>
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860.535.2080
> www.fpdc.com
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum             
>                           
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to