I'm not aware of a specific prohibition, and NFPA 13 2010 "6.7.4.3.1* Systems 
that have more than one control valve that must be closed to work on a system 
or space shall have a sign referring to existence and location of other 
valves." would suggest to me it's OK as long as that requirement is met?

Mike Morey, SET, CFPS
Sprinkler Designer
BMW Constructors, Inc.
O: 317.651.0596 | C: 317.439.2695
www.bmwc.com



-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org on behalf of Ronl.Fletcher
Sent: Wed 10/26/2011 1:13 PM
To: sprinklerforum@firesprinkler.org
Subject: Dual floor control assembies
 
Is anyone aware of a prohibition against having two floor control assemblies  
on each floor connected to two different standpipes and calculating the loop to 
size the sprinkler main?


Ron Fletcher
Aero Automatic
Phoenix, AZ