Hello Ronl.Fletcher, There are a few high rises here setup that way around here... BIG thing is the alarm company has to put the flow switches on different points so it can be verified that BOTH work during the test. Inspectors need to know to look for 2 flow alarms from each floor and have a way to verify they both work.
Wednesday, October 26, 2011, 1:13:51 PM, you wrote: > Is anyone aware of a prohibition against having two floor control > assemblies on each floor connected to two different standpipes and > calculating the loop to size the sprinkler main? > Ron Fletcher > Aero Automatic > Phoenix, AZ > _______________________________________________ > Sprinklerforum mailing list > Sprinklerforum@firesprinkler.org > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum -- Best regards, Charles mailto:charl...@mbfsg.com Confidentiality Notice: This e-mail message, including any attachments, is for the sole purpose of the intended recipients and may contain confidential and privileged information. Any unauthorized review, use, disclosure or distribution is prohibited. If you are not the intended recipient, please contact the sender by reply e-mail and destroy all copies of the original message. _______________________________________________ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum