Hello Ronl.Fletcher,

There are a few high rises here setup that way around here... BIG thing is the 
alarm company has to put the flow switches on different points so it can be 
verified that BOTH work during the test. Inspectors need to know to look for 2 
flow alarms from each floor and have a way to verify they both work.

Wednesday, October 26, 2011, 1:13:51 PM, you wrote:

> Is anyone aware of a prohibition against having two floor control
> assemblies  on each floor connected to two different standpipes and
> calculating the loop to size the sprinkler main?


> Ron Fletcher
> Aero Automatic
> Phoenix, AZ