Assuming a SSU, you need to be 3x the diameter of the pipe away. So, your 
deflector would need to be 13.5" away from the top of the pipe. That 
measurement is on the diagonal, so you could arm out the side and up so the 
distance hits 13.5". There is also an exception to the 3x rule, that in light 
and ordinary hazard areas, only structural members shall be considered for the 
3x rule. So, using that allowance, the sprinkler could be directly on the pipe 
if you have an SSU in a light or ordinary hazard area. 

Happy Thanksgiving!

Travis Mack
MFP Design, LLC
480-505-9271
Sent from my iPad

On Nov 24, 2011, at 8:34 AM, Cory Power <[email protected]> wrote:

> Does anyone know the minimum distance an upright can be above of a 4" main. 
> it will be coming off a 4 x 1 on a dry system. There isn't much room.