It's a holiday and I'm not obliged to reference (my personal rule of the day) but isn't there also a rule about not attaching a uprights directly to pipe 3" nom and over? OK, broker my new rule since I'm just sitting around waiting for orders from the Commander of Thanksgiving anyways. NFPA 13-2010 ed. 8.6.5.2.1.8 exempts piping less than 3" from the 3x rule, otherwise.... And that rule has always (always is at least 1999 edition if not older) been there. (Big change editions to 13 I recall 1954, 1991, 1999, and everything this century). Happy National Eating Day. Do take a moment to reflect about those hat are going hungry in this country where we throw more food away per capita than most of the world produces, and how you feel about that. Are you an "every man for himself" type or a "we're all in this boat together" person? Or somewhere in between? We show a collective appearance to the world that is a composite of "me plus us" to one degree or another. Like going to a date are you satisfied with the way we look, or not, or don't care? Sorry to talk politics (but not partisan mind you) but I'm feeling thankful and ashamed at the same time.
On Thu, Nov 24, 2011 at 8:21 AM, Travis Mack <[email protected]> wrote: > Assuming a SSU, you need to be 3x the diameter of the pipe away. So, your > deflector would need to be 13.5" away from the top of the pipe. That > measurement is on the diagonal, so you could arm out the side and up so the > distance hits 13.5". There is also an exception to the 3x rule, that in > light and ordinary hazard areas, only structural members shall be > considered for the 3x rule. So, using that allowance, the sprinkler could > be directly on the pipe if you have an SSU in a light or ordinary hazard > area. > > Happy Thanksgiving! > > Travis Mack > MFP Design, LLC > 480-505-9271 > Sent from my iPad > > On Nov 24, 2011, at 8:34 AM, Cory Power <[email protected]> > wrote: > > > Does anyone know the minimum distance an upright can be above of a 4" > main. it will be coming off a 4 x 1 on a dry system. There isn't much room. > > -------------- next part -------------- > > An HTML attachment was scrubbed... > > URL: < > http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111124/81ef0e9e/attachment.html > > > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 [email protected] http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111124/d1c6f989/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum