Not hardly.  As stated if it's true Crude oil it's typically a IB.   Water will 
be a joke.  Not having all the details but I'd be strongly looking at 
Foam/water (NFPA 16) as the minimum.

It would be worth asking the person whose Professional Stamp is on it what they 
based that criteria on.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Robert Thompson
Sent: Friday, December 09, 2011 10:09 AM
To: [email protected]
Subject: Good one for a Friday

Indoor rail car loading of crude oil.  design dry system water only .3/6000 
sqft at deck and under obstructions.  100 sqft spacing of 11.2k sprinklers.  
Right track or way off.   Don't see everyday but may in future.

Thank You
Robert Thompson
Certified Engineering Technologist

Dakota Fire Protection
1710 North Washington Street
Grand Forks, ND 58203
Phone: 701-772-8820
Fax: 701-772-7932
Email: [email protected]




-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111209/a526975d/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to