The confusion started when 25 said flow the most remote hose connection. Some focused on the fact that it used the singular tense verses plural so obviously they only had to flow from ONE outlet and since an outlet only has to flow 250 gpm THAT was the amount to flow for the test. DOH!

Roland

On Dec 29, 2011, at 6:14 AM, Todd Williams wrote:

I am working with a hospital with a total of 9 standpipes. There are standpipes that are both pre and post 1993. The original building is partially sprinklered and the new section is fully sprinklered.

1. Is the intent of NFPA 25 that multiple standpipes be flowed simultaneously to meet the 1250 gpm demand?

2. Should the two sections of the hospital be flow independent of each other?

3. If yes to 1 and 2, could the new section be flowed as a fully sprinklered building (thus 1000 gpm) as opposed to 1250?

4. How should i handle pipe schedule standpipes, if any exist?

I haven't had to deal with 5 year standpipe tests before.

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com