I does in this situation. It is an existing system with a new underground 
configuration. With all the sprinklers included, we are right at 0. 


At 11:47 AM 1/6/2012, you wrote:
>Is omitting those sprinklers going to make much of a difference in the calcs?
>
>Craig L. Prahl, CET   
>Fire Protection 
>CH2MHILL
>Lockwood Greene
>1500 International Drive
>Spartanburg, SC  29304-0491
>Direct - 864.599.4102
>Fax - 864.599.8439
>CH2MHILL Extension  74102
>[email protected]
>
>
>-----Original Message-----
>From: [email protected] 
>[mailto:[email protected]] On Behalf Of Todd Williams
>Sent: Friday, January 06, 2012 11:31 AM
>To: [email protected]
>Subject: Omitting sprinklers from calculations - small buildings
>
>NFPA 13 (2007) states that some small rooms with single sprinklers can be 
>omitted from hydraulic calculations, provided at least the minimum areas of 
>figure 11.2.3.1.1 are met. I am working on a 1200 sqft LH building that has a 
>system in it. According to the book, I have to include sprinklers in the 
>closets in my calculations. Any reason why maximum building areas less than 
>the 11.2.3.1.1 minimums would not be a consideration for this exclusion?
>
>Todd G. Williams, PE
>Fire Protection Design/Consulting
>Stonington, CT
>860.535.2080
>www.fpdc.com
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to