Is this one of those deals where if the closets weren't there the area would be covered and only have sprinklers inside because they're separated from the area the other sprinklers cover? So you have four heads in the design area that wouldn't normally be there except for the closet, and those four heads kill the calcs? This is one that always kills me and so I'd like to see the collective wisdom. Seems to me that if the fire is in the closet the head inside will play havoc with it and if it breaches to the outside (door open), even with another head in the main area opening there isn't a big chance of being overwhelmed. Or if the fire starts outside and moves into the closet the same but in reverse. But I'm just guessing.
On Fri, Jan 6, 2012 at 9:57 AM, Todd Williams <[email protected]> wrote: > Check your aeronautics. There are 4 closets in this building. Not flowing > 2 of them gets us up to 5 psi. (Actually started with 0.342 psi under the > curve) > > At 12:46 PM 1/6/2012, you wrote: > >sounds like that plane won't fly regardless of omitting the closet. > >Don't forget you can use a K-2.8 in the closet. That should get you > >up to a 0.2. > > > >Roland > > > >On Jan 6, 2012, at 9:00 AM, Todd Williams wrote: > > > >>I does in this situation. It is an existing system with a new > >>underground configuration. With all the sprinklers included, we are > >>right at 0. > > > >_______________________________________________ > >Sprinklerforum mailing list > >[email protected] > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > Todd G. Williams, PE > Fire Protection Design/Consulting > Stonington, CT > 860.535.2080 > www.fpdc.com > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 [email protected] http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120106/302a9722/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum