NFPA 13 (2007) states that some small rooms with single sprinklers can be 
omitted from hydraulic calculations, provided at least the minimum areas of 
figure 11.2.3.1.1 are met. I am working on a 1200 sqft LH building that has a 
system in it. According to the book, I have to include sprinklers in the 
closets in my calculations. Any reason why maximum building areas less than the 
11.2.3.1.1 minimums would not be a consideration for this exclusion?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com