I've never seen or done it...

Jeff Garrison
On Jan 16, 2012 9:39 AM, "C&H Fire - Mike Gallello" <[email protected]>
wrote:

> Ok, another absurd question...
>
> Background:
> Consider a dry standpipe system (Galvanized Sh40 throughout) in a
> parking garage, 6 stories open air structure, core slab / concrete.
> Class III Standpipe required but no sprinkler requirement, we have 6
> vertical standpipes, 3 of which are located in the stairwells.
>
> With that being said, 2010 14 - 6.1.2.2 States that "Standpipes and
> lateral piping supplied by standpipes shall be located in enclosed exit
> stairways or shall be protected by a degree of fire resistance equal to
> that required for enclosed exit stairways in the building in which they
> are located."
>
> There are 3 stairwells within this parking structure which are rated for
> 2 hours, just like most of the other exits and access to egress required
> ratings.
>
> This has been in the code for a while, but it's rare that we've been
> stuck doing this and even more rare that the mechanical consultant has
> pushed for this.  They are saying 45 min based on nothing, I'm saying
> don't bother doing it, but if you do it should be to code and have the
> full 2 hour per NFPA 14.
>
> Absurd Question:
> Is anyone actually doing this?  Is there an amendment or errata to NFPA
> 14 to ditch this?  I can't count how many installations I've seen (and
> done) that have no fire resistance wrap or anything installed after the
> fact, or has ever been questioned really.  I've only been doing this for
> around 15 years and this is a first for me.  I don't even want to look
> at pricing for 2 hour wrap for around 300 feet horizontal and 6x3
> standpipes around 60' each.
>
> Mike Gallello
> [email protected]
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120116/e36d813f/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to