Why isn't the FDC supplying an automatic wet standpipe system considered
supplemental as well then?  The required demand for the standpipes are
met by the sprinkler system but NFPA 14 still requires a 2 1/2"
connection for every 250gpm demand?
Dewayne

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: Wednesday, February 01, 2012 10:09 AM
To: [email protected]
Subject: Re: Standpipe FDC Inlets

but the FDC on a sprinkler system is SUPPLEMENTAL and you don't have to
meet the system demand.

Since one has to also calc the system demand from the FDC, has anyone
looked at the maximum flow they can get through a single 2-way FDC and
still meet their design demand?

Roland

On Feb 1, 2012, at 7:52 AM, Steve Leyton wrote:

> As do a few on the left side.  It's common to see demand-based  
> requirements for both standpipe and sprinkler systems.   How many  
> ESFR systems are out there with 2-way FDC's?   If system demand is  
> 1,600gpm ...
>
> SL