I will need some guidance on how to calculate the "supplemental" flow not full 
flow through an FDC.

Ron Fletcher
Aero Automatic
Phoenix, AZ




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Roland Huggins
Sent: Thursday, February 02, 2012 8:17 AM
To: [email protected]
Subject: Re: Standpipe FDC Inlets

It isn't appropriate for 13 to change?  Just because it is the same piece of 
equipment doesn't mean that they have the same objectives or levels of 
criticality.

Try submitting a proposal next cycle showing the friction loss and try to 
change it.  WHat is the loss at 250 gpm and 500 gpm?

Roland

On Feb 2, 2012, at 5:30 AM, <[email protected]> wrote:

> Maybe because the 14 committee knows there is no way to "supplement"  
> the water supply. If the pressure and flow at the FDC is great enough 
> to open the check valve it will close the riser check. While I don't 
> agree with the 250 gpm for each inlet, 500 is more reasonable. 13 
> should drop "supplemental" altogether or replace it with something 
> more realistic.
>
>
> Ron Fletcher
> Aero Automatic