When an entire facility does not require fixed sprinkler systems and a single 
9x12 room is classified as an "H" occupancy due to non-combustible/flammable 
gases, corrosives or other non-fire hazard, it is not uncommon to receive a 
variance for omission of sprinklers for that one room.  Requesting relief for 
providing a municipal tap, run-in, riser and piping for one or two sprinklers 
for an area where there is no greater fire hazard than any adjacent area is 
often not challenged by most reasonable AHJ's.  

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Bruce Verhei
Sent: Monday, February 06, 2012 5:10 PM
To: [email protected]
Subject: Re: SO2 chemical

....architect should have evaluated quantity in storage and use. 

If H, minimum design criteria for building is OH-2, unless some other factor 
drives higher criteria. 

Sent from my Motorola ATRIX™ 4G on AT&T

-----Original message-----
From: Bruce Verhei <[email protected]>
To: [email protected]
Sent: Mon, Feb 6, 2012 22:06:58 GMT+00:00
Subject: Re: SO2 chemical

IBC?

Has occupancy class been determined? SO2 is a hazardous material.  Architect

Sent from my Motorola ATRIX™ 4G on AT&T

-----Original message-----
From: Douglas Hicks <[email protected]>
To: [email protected]
Sent: Mon, Feb 6, 2012 21:27:33 GMT+00:00
Subject: SO2 chemical

The city is asking if  sprinkler coverage is needed at the sewage treatment 
plant.  Of particular concern is a room (8 x 12) where the chlorine in the 
sewage is treated with SO2 (sulfur dioxide) so the discharge is rendered safe 
to be put into the river.  The building construction is a combination of wood 
and brick.  I do not know any dimensions of the entire building or other rooms. 
 At present, there is a sprinkler head in the SO2 room, plumbed off the potable 
water supply.  No shut off valves, no gauges, no drains.  

My initial response is if a sprinkler system is needed, it would be addressed 
by the city’s insurance carrier.  

Anyone familiar with a sprinkler in treatment plants?
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120206/1e03f3f1/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120206/fd802042/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to