I believe there were 2 separate recalls; one for Omegas and one for O-rings. 
Were they both voluntary? I was under the impression that one was mandatory and 
one voluntary. 


At 10:42 AM 2/17/2012, you wrote:
>Perfect - thanks
>
>On Fri, Feb 17, 2012 at 9:41 AM, Cahill, Christopher
><[email protected]>wrote:
>
>> It is not voluntary any more:
>> IFC 901.10 Recall of fire protection components.
>> Any fire protection system component regulated by this code that is the
>> subject of a voluntary or mandatory recall under federal law shall be
>> replaced with approved, listed components in compliance with the referenced
>> standards of this code. The fire code official shall be notified in writing
>> by the building owner when the recalled component parts have been replaced.
>>
>> Owner is liable as long as the inspection reported it.
>>
>> Insurance can't actually require anything.  It's a contract.  Best they
>> can do is say do something or find a different insurance company.
>>
>> Chris Cahill, PE*
>> Senior Fire Protection Engineer, Aviation & Facilities Group
>> Burns & McDonnell
>> 8201 Norman Center Drive
>> Bloomington, MN 55437
>> Phone:  952.656.3652
>> Fax:  952.229.2923
>> [email protected]
>> www.burnsmcd.com
>>
>> Proud to be one of FORTUNE's 100 Best Companies to Work For
>> *Registered in: MN
>>
>>
>>
>>
>>
>> -----Original Message-----
>> From: [email protected] [mailto:
>> [email protected]] On Behalf Of Greg McGahan
>> Sent: Friday, February 17, 2012 9:30 AM
>> To: [email protected]
>> Subject: Central Head Recall
>>
>> Can anyone update me on the following questions (brought to me via a
>> concerned AHJ):
>>
>> 1) The Central Head recall is voluntary - still ?
>> 2) If the recalled heads are not replaced - who is liable in the event of
>> an event? The AHJ for not requiring the change?
>> 3) Did a lot of insurance companies require head replacement?
>>
>> Thanks for the help...evidently there is a local competitor that has found
>> some and is telling the owner that the Head Replacement is mandatory and
>> MUST be performed immediately.
>>
>> Greg
>>
>> --
>> Greg McGahan
>> Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
>> 1160 McKenzie Road
>> Cantonment, FL 32533
>> 850-937-1850
>> fax 850-937-1852
>> -------------- next part --------------
>> An HTML attachment was scrubbed...
>> URL: <
>> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120217/f4946139/attachment.html
>> >
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>
>
>
>-- 
>Greg McGahan
>Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
>1160 McKenzie Road
>Cantonment, FL 32533
>850-937-1850
>fax 850-937-1852
>-------------- next part --------------
>An HTML attachment was scrubbed...
>URL: 
><http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120217/ac2f1fbf/attachment.html>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to