1.  Being OK for electrical doesn't automatically make it OK for
electronics or systems with moving parts.

3.  Continued training and awareness can't be counted on.  George Church's
anecdote about the fire alarm in a restaurant proves that people are dumber
than sheep.  Sheep will at least follow the leader.

4.  There isn't always a huge mess.  Just because aerosol might not be
worse than some of its competitor doesn't make the method of choice.

Ed Vining
4819 John Muir Rd
Martinez CA 94553
925-228-8792
Cell 925-787-0465


On Mon, Apr 30, 2012 at 12:17 PM, Reza Esmaeili
<[email protected]>wrote:

>
>
>
>
>
> I have contacted Firepro which is making UL listed Aerosol units and asked
> them the below questions, I would appreciate your comments on their answers:
>
> 1- According to NFPA 2010 "Aerosol fire-extinguishing agents shall not be
> used on fires involving Deep-seated fires in Class A materials", then do
> you offer Firepro units to be used in Paper/Book Archive Rooms facing deep
> seated fire in class A material?
> ANSWER: All fixed gas extinguishing systems, as well as aerosol systems
> are tested and certified for Class A, surface burning fires. The test
> protocols for polymeric materials and wood specify pre-burning times from
> 3.5 min. to 6 min. respectively. Longer burning time is considered as deep
> seated fires.
>
> 2- According to NFPA 2010 "The potential adverse effects of agent
> particulate residue on sensitive equipment shall be considered", then do
> you offer Firepro units to be used in Server Rooms with sensitive hard
> disks.
> ANSWER: FirePro has been independently tested by NLR (Dutch National
> Aerospace Laboratory) and TNO (Netherlands Organisation for Applied
> Scientific Research), proving that there are no effects on (a) corrosion of
> sensitive electrical components, and (b) the operation of electrical
> equipment, respectively.
>
> 3- According to NFPA 2010 "aerosol systems shall be used in normally
> unoccupied areas because of visibility obscuration and the potential health
> effects of accidental exposure to the agent"  then do you offer Firepro
> units to be used in Monitoring Rooms where people usually exist?
> ANSWER: Please see detailed response
> www.esmaeili.ir/Aerosol-in-occupied-areas.pdf
>
> 4- Do you offer Firepro units to be in a place where dust or residue is a
> matter of concern and clean-up procedure costs too much like a museum, art
> gallery?
> ANSWER:  Please note, after a fire, there is a huge mess, Therefore, after
> a fire, you are going to clean anyway ! FirePro has been used in museums
> and old cultural buildings, etc,  the consequences of other extinguishing
> agents such as halocarbons, especially in electrical/electronic
> applications, can be more serious; of paramount importance is the
> liberation/formation of HF (hydrogen fluoride) and CO at high temperatures.
> So it is best to sweep/dust the FP particles than to damage/destroy the
> electrical components with the decomposition of halocarbons/FM-200.
>
>
> Best,
> Reza
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120430/aca9680e/attachment.html
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120430/55489afc/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to