Check NFPA 15 Table 6.1.2.2 for electrical clearances from water spray
equipment to live un-insulated electrical components. Also it is very
good practice to check with the owner's engineering department of the
electrical equipment since they have the safe operating distances as
part of the design of the equipment. It is important to check with the
supplier of the electric power to see what safeguards are required.
Have a fire safe day.
Jim
DAVIDSON ASSOCIATES
Fire Protection Engineering P. O. Box 4010
Code Consultants Greenville, DE 19807-0010
Medical Gas Systems Engineering (302) 994-9500
Fax (302) 234-1781
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ford,
Charles
Sent: Friday, May 04, 2012 8:00 AM
To: [email protected]
Subject: RE: High voltage clearances
I thought NFPA 13 had a chart specifying clearance distance from
sprinkler piping and hi voltage open bus bars. I can't find it. There is
one in 12 ( co2 systems) but not eaxctly the same thing. I have a
partner asking if there is a minimum distance. any thoughts out there?
C. Burton Ford
Nicet Certified
Special Hazards IV
Fire alarm IV
Sprinkler III
Water Based Inspections I
NFPA Certified Fire Protection Specialist [CFPS] Cintas Fire Protection
1038 Conshohocken Road
Conshohocken ,PA 19428
610-233-1400
Fax 610-233-1401
________________________________________
From: [email protected]
[[email protected]] On Behalf Of Stewart Kidd
[[email protected]]
Sent: Monday, April 30, 2012 6:26 PM
To: [email protected]
Subject: Re: Aerosol vs Halocarbon/Inert extinguishing agents - Firepro
Answers - Please comment!
Reza
1. Why does IBM use sprinklers (with water) in all its factories and
units ?
2.Data can be recovered from hard drives which have been wetted by
sprinklers or fire hoses - this is not true of powders 3. Clean up of
powder even when there has been no fire is very expensive as the powder
is hygroscopic.
4. Tests in Norway and by US GSA suggest that powder is damaging for
heritage objects - especially paintings, glass and china
Best
Stewart
On 30 Apr 2012, at 20:34, Ed Vining wrote:
> 1. Being OK for electrical doesn't automatically make it OK for
> electronics or systems with moving parts.
>
> 3. Continued training and awareness can't be counted on. George
> Church's anecdote about the fire alarm in a restaurant proves that
> people are dumber than sheep. Sheep will at least follow the leader.
>
> 4. There isn't always a huge mess. Just because aerosol might not be
> worse than some of its competitor doesn't make the method of choice.
>
> Ed Vining
> 4819 John Muir Rd
> Martinez CA 94553
> 925-228-8792
> Cell 925-787-0465
>
>
> On Mon, Apr 30, 2012 at 12:17 PM, Reza Esmaeili
> <[email protected]>wrote:
>
>>
>>
>>
>>
>>
>> I have contacted Firepro which is making UL listed Aerosol units and
>> asked them the below questions, I would appreciate your comments on
their answers:
>>
>> 1- According to NFPA 2010 "Aerosol fire-extinguishing agents shall
>> not be used on fires involving Deep-seated fires in Class A
>> materials", then do you offer Firepro units to be used in Paper/Book
>> Archive Rooms facing deep seated fire in class A material?
>> ANSWER: All fixed gas extinguishing systems, as well as aerosol
>> systems are tested and certified for Class A, surface burning fires.
>> The test protocols for polymeric materials and wood specify
>> pre-burning times from
>> 3.5 min. to 6 min. respectively. Longer burning time is considered as
>> deep seated fires.
>>
>> 2- According to NFPA 2010 "The potential adverse effects of agent
>> particulate residue on sensitive equipment shall be considered", then
>> do you offer Firepro units to be used in Server Rooms with sensitive
>> hard disks.
>> ANSWER: FirePro has been independently tested by NLR (Dutch National
>> Aerospace Laboratory) and TNO (Netherlands Organisation for Applied
>> Scientific Research), proving that there are no effects on (a)
>> corrosion of sensitive electrical components, and (b) the operation
>> of electrical equipment, respectively.
>>
>> 3- According to NFPA 2010 "aerosol systems shall be used in normally
>> unoccupied areas because of visibility obscuration and the potential
>> health effects of accidental exposure to the agent" then do you
>> offer Firepro units to be used in Monitoring Rooms where people
usually exist?
>> ANSWER: Please see detailed response
>> www.esmaeili.ir/Aerosol-in-occupied-areas.pdf
>>
>> 4- Do you offer Firepro units to be in a place where dust or residue
>> is a matter of concern and clean-up procedure costs too much like a
>> museum, art gallery?
>> ANSWER: Please note, after a fire, there is a huge mess, Therefore,
>> after a fire, you are going to clean anyway ! FirePro has been used
>> in museums and old cultural buildings, etc, the consequences of
>> other extinguishing agents such as halocarbons, especially in
>> electrical/electronic applications, can be more serious; of paramount
>> importance is the liberation/formation of HF (hydrogen fluoride) and
CO at high temperatures.
>> So it is best to sweep/dust the FP particles than to damage/destroy
>> the electrical components with the decomposition of
halocarbons/FM-200.
>>
>>
>> Best,
>> Reza
>> -------------- next part -------------- An HTML attachment was
>> scrubbed...
>> URL: <
>> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/atta
>> chments/20120430/aca9680e/attachment.html
>>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
> -------------- next part -------------- An HTML attachment was
> scrubbed...
> URL:
> <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/atta
> chments/20120430/55489afc/attachment.html>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
This e-mail transmission contains information that is intended to be
confidential and privileged. If you receive this e-mail and you are not
a named addressee you are hereby notified that you are not authorized to
read, print, retain, copy or disseminate this communication without the
consent of the sender and that doing so is prohibited and may be
unlawful. Please reply to the message immediately by informing the
sender that the message was misdirected. After replying, please delete
and otherwise erase it and any attachments from your computer system.
Your assistance in correcting this error is appreciated.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum