Maybe if you'd up the ante by offering to put something else on the chopping 
block?


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Brad Casterline
Sent: Wednesday, May 09, 2012 2:52 PM
To: [email protected]
Subject: RE: Adjusting Pump Curves for Pump Speed

Mr. Brooks,

Where it comes to de-mystifying fire pumps, there is nothing like using feet 
and seconds only, and putting gravity back in. It makes the affinity laws, 
which is the subject of your post, especially clear.
If you would, please, post the rated pressure for the 3450 rated speed, and I 
will put my pride on the Forum Chopping Block by posting the impeller diameter. 
I do not want or need the rated GPM to do this (I would have to have GPM to 
post the rated horsepower though). My intent here is to help Forumites see how 
clean and simple all things sprinkler calc can be, and if I can do it, anybody 
can.
If you do not have the time or interest it is fine-- i posted something similar 
a couple years ago.

Brad Casterline

-----Original Message-----
From: George Church [mailto:[email protected]]
Sent: Wednesday, May 09, 2012 1:49 PM
To: [email protected]
Subject: RE: Adjusting Pump Curves for Pump Speed

Its exponential- small bump in speed can give amazing results :) when you find 
yourself a little short.
Yes, our driver WAS listed for the higher speed back in 1968....

George L.  Church, Jr., CET
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bill Brooks
Sent: Wednesday, May 09, 2012 12:32 PM
To: [email protected]
Subject: RE: Adjusting Pump Curves for Pump Speed

Thanks, age is a good thing in some products, but ...

Bill Brooks


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: Wednesday, May 09, 2012 12:20 PM
To: [email protected]
Subject: RE: Adjusting Pump Curves for Pump Speed

See NFPA 20, A.14.2.5.4(7)(f) on page 90 of the 2010 ed.


Steve Leyton




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bill Brooks
Sent: Wednesday, May 09, 2012 9:11 AM
To: [email protected]
Subject: Adjusting Pump Curves for Pump Speed

This is something I should know, but how are pump curves adjusted for pump 
speed?  I'm looking at a curve based on 3450 rpm (60 Hz) and want to adjust it 
for 2900 rpm (50 Hz).  Is this possible?

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell 


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to