Good question! 2010 says 3 to 7.5 feet also. I checked the ROP for next edition and did not see any thing about it. Technically if the beams are less than 3' it is not Beam and Girder. Panel Construction does not have the 3' min., but if it exceeds 300 S.F. it is not obstructed. Very curious situation, I hope someone can shed some light.
-----Original Message----- From: Dewayne Martinez [mailto:[email protected]] Sent: Friday, May 11, 2012 10:36 AM To: SprinklerFORUM Subject: Obstructed construction NFPA 13 (07ed) section A3.7.1 (1) When beams are less than 3 ft o.c. do the rules for obstruction construction still apply or does the pocket between the beams become small enough to treat it like unobstructed construction and place the sprinkler deflector 1-12" below the beams? Thanks, Dewayne Martinez Design Build Fire Protection 262-784-7900 (w) 262-784-8401 (f) 414-349-0468 (cell) -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment s/20120511/0cdf6405/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum