I doubt you can justify exceeding 6" below the plane of the bottom of the
beams though!

-----Original Message-----
From: Brad Casterline [mailto:[email protected]] 
Sent: Friday, May 11, 2012 11:37 AM
To: [email protected]
Subject: RE: Obstructed construction

Good question! 2010 says 3 to 7.5 feet also. I checked the ROP for next
edition and did not see any thing about it. Technically if the beams are
less than 3' it is not Beam and Girder. Panel Construction does not have the
3' min., but if it exceeds 300 S.F. it is not obstructed. Very curious
situation, I hope someone can shed some light. 

-----Original Message-----
From: Dewayne Martinez [mailto:[email protected]] 
Sent: Friday, May 11, 2012 10:36 AM
To: SprinklerFORUM
Subject: Obstructed construction

NFPA 13 (07ed) section A3.7.1 (1)

When beams are less than 3 ft o.c. do the rules for obstruction
construction still apply or does the pocket between the beams become
small enough to treat it like unobstructed construction and place the
sprinkler deflector 1-12" below the beams?

 

Thanks,

Dewayne Martinez

Design Build Fire Protection

262-784-7900 (w)

262-784-8401 (f)

414-349-0468 (cell)

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120511/0cdf6405/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to