We have run into this a few times. It takes a call to the AHJ. If the beams are 
more than 22" deep I would say you should maintain a 1" deflector distance 
below the beams. I believe that the concrete twin tee rule is only thing that 
allows greater than 22". The 3 ft rule has been in 13 forever (I think) and 
doesn't make much sense. It is even in the concrete twin tees. A strict 
interpretation would require a head in every pocket if the beams are less than 
3 ft. on center. Maybe when this happens it should be treated like a smooth 
ceiling?

The last project we had this on was concrete twin tees 34" deep with the stems 
18" apart. The AHJ agreed that we should stay within 1" of the bottom of the 
tees.


Ron Fletcher
Aero Automatic
Phoenix, AZ


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Dewayne Martinez
Sent: Friday, May 11, 2012 8:36 AM
To: SprinklerFORUM
Subject: Obstructed construction

NFPA 13 (07ed) section A3.7.1 (1)

When beams are less than 3 ft o.c. do the rules for obstruction construction 
still apply or does the pocket between the beams become small enough to treat 
it like unobstructed construction and place the sprinkler deflector 1-12" below 
the beams?

 

Thanks,

Dewayne Martinez

Design Build Fire Protection

262-784-7900 (w)

262-784-8401 (f)

414-349-0468 (cell)

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120511/0cdf6405/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to