If you follow the gas piping rules you'd use coated black steel, threaded, with 10 mil (maybe more, I don't recall without a book to reference) wrapping around the fittings, then tarred (again I think). Or, special dispensation from your local Pope, and use Blazemaster while underground. Comes in 3" (I believe that's what you'd said you were planning to use, is not under any threat from fire underground, doesn't corrode, and flows better. The kicker is not being listed for the purpose though I'd bet only because it hasn't been tested for this application.
On Mon, Jul 30, 2012 at 3:59 PM, Mark Sornsin <[email protected]>wrote: > Greg: > > NFPA 13 forbids steel pipe underground, with the exception of 'dry' FDC > piping. In that case you are allowed to use galvanized. Don't recall all of > the specifics (like if wrapping is required). But to your point the > problem is corrosion - the galvanizing doe, then tsn't help much > underground. However, I don't know why a properly wrapped pipe couldn't do > just fine underground. Except that 'properly wrapped' may be too difficult > to achieve...? There may be too much risk of an Achilles heel in the form > of an unprotected surface somewhere along the run. > > So how about cut-grooved ductile iron instead? > > Mark A. Sornsin, PE| Fire Protection Engineer > Ulteig Engineers, Inc.| Fargo, ND > [email protected] > > -----Original Message----- > From: [email protected] [mailto: > [email protected]] On Behalf Of Gregory Lindholm > Sent: Monday, July 30, 2012 3:10 PM > To: SprinklerFORUM > Subject: Galvanized underground main > > > I think I have seen this before, but could not find it. > > We need to run a wet main underground from one building to another. They > are about 15' apart. The main will be 7' deep to get below frost. We plan > to run 3" galv. sch. 40 with galv. grooved fittings. There will only be 2 > ell & 4 couplings underground, and plan to wrap it with what the plumber > use to wrap underground. > > Is there anything wrong with this idea, either code or common sense? > > Greg Lindholm > -------------- next part -------------- > An HTML attachment was scrubbed... > URL: < > http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120730/e7a4d52d/attachment.html > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 [email protected] http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120730/390475fc/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum