Ron, stop it. It's a condition that is known to impede sprinkler operation. Doesn't matter if the AHJ prescribed it - which they very well may have not. Most of these installations were by lazy contractors trying to shorten drops in future TI work. Some cultures still use human teeth for currency, but that doesn't make it right. As the AHJ's like to say, "Just because we did it wrong before doesn't make it right now."
SML -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Ron Greenman Sent: Thursday, August 02, 2012 9:57 AM To: [email protected] Subject: Re: NFPA 25 inspection of sprinklers with heat collector plates installed It's a deficiency for sure, but not per 25. I keep going back in my mind to the tech that pointed out a coverage deficiency in coverage that he saw in one part of the building, and called out as such within the test reports themselves, rather than as comments, but missed a similar deficiency elsewhere. After the building burnt due to the deficiency that he missed the lawyer convinced the jury that the tech was practicing engineering without a license, that the owner had a perfect right to expect that a complete engineering review had been done as the tech acted like an engineer and made at least one engineering call. End result was a $12M judgement over a couple hundred dollar inspection. I think George told us all about this originally. And this is merely the worst case. Heat collectors, old or new are, are a design/layout issue and so allowed or denied by the AHJ. The owner needs to be informed of the questionability of the efficacy, and perhaps the AHJ directly, dependent on the rules regarding reporting within the jurisdiction, but hey are not something that a tech can decide need to be/should be there or not. On Thu, Aug 2, 2012 at 9:44 AM, <[email protected]> wrote: > Gentlemen: > > Good points...Did you say it had the 'UL' symbol or the 'FM' symbol??? > Oh, then they shouldn't be attached to the sprinkler, the sprinkler > system, the piping (or anything else) - per NFPA-13 (starting in > 1896??)...It's a "deficiency" in my non-PE opinion. > > Regards to all. > > Jerry > [email protected] > > Jerry D. Watts, SFPE > President & Co-Founder > ACCENT FIRE ENGINEERING INT'L. Ltd.* > Santa Fe/Albuquerque/Silver City/Roswell/Artesia New Mexico Seattle, > WA San Diego, CA Phoenix, AZ > (800) 503.1961 > > *Licensed Fire Engineers - Architects/Inspectors/Fire Investigators: > AZ CA CO NM NV HY TX UT KS MD MS > -------------- next part -------------- An HTML attachment was > scrubbed... > URL: < > http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attac > hments/20120802/38e62130/attachment.html > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 [email protected] http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach ments/20120802/af6c912c/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum