One big problem is design professionals who don't know to ask for MSDS or who 
can't read them when they get them.

I didn't read that the scenario in question was a mercantile operation.


Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Bill Brooks
Sent: Monday, August 13, 2012 10:39 AM
To: [email protected]
Subject: RE: 02 storage (hazardous materials assessment)

The definition of O2 as a hazardous material is based on IBC Section 307.2
and the defined quantities in IBC Table 307.1(1).  When quantities exceed
the MAQ in Table 307.1(1), the various design options being discussed come
into play.  The concept of Control Area is defined in (2009) IBC Section
414.2. The IBC fire barrier is noted in Table 414.2.2.

I'm very surprised any AHJ would have to be educated on this, but looking
back at the messages it may be that what the AHJ said was being filtered
through a number of people who were not familiar with the process used to
deal with hazardous materials.

What I've found in the real world is the lack of correlation between
commonly generated MSDS and the various building and fire code
classification tables which does not appear to factor into this application.

I'm not familiar with the Florida Building Code, perhaps it is much more
complex than the IBC.

Keep in mind there are 13 Exceptions listed under Section 307.1, one of
which (Exception 2) is the storage of flammable and combustible liquids in
mercantile. If it were not for this exception some stores we regularly shop
in would not exist in their present form. Also Exception 6 is your
neighborhood State Store (a nod to George C.).

Bill Brooks

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bill Brooks
Sent: Friday, August 10, 2012 3:05 PM
To: [email protected]
Subject: RE: 02 storage

Sounds like there are some building code issues which should not be
addressed by the sprinkler contractor. It may be your job is not so
complicated if you apply NFPA 55.  But somebody else may or may not have
done their job.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Friday, August 10, 2012 2:39 PM
To: [email protected]
Subject: Re: 02 storage

IFC, chapter 27 and NFPA 55 have the same criteria for oxidizing gas.  It is
3000 cu ft per control area.  Don't know where the AHJ is coming up with
12000 cu ft unless he is considering the maximum of 4 control areas per
building and then you get to 12000 cu ft.  This means 4 areas that are fire
separated from each other and the rest of the building.

John Hoffman P.E. | Fire Protection Engineer | Facility Engineering
Services, KCP, LLC - Burns & McDonnell Engineering | National Nuclear
Security Administration's Kansas City Plant | Operated by Honeywell FM&T |
2000 E. 95th St | Kansas City, MO  64131 | ph 816-997-7213 |
[email protected]



From:   Greg McGahan <[email protected]>
To:     [email protected]
Date:   08/10/2012 12:50 PM
Subject:        02 storage
Sent by:        [email protected]



This is a completely new area for me so any help is appreciated.

Issue:  Medical Gas Storage of 02 only in various cylinders.

The tenant and owner of this Commercial / Industrial Strip center is having
difficulty with the AHJ who claims that even if they classify the warehouse
portion of this space as Storage Occupancy instead of Business, The maximum
cubic footage of 02 allowed to be stored in one place is 12,000 with "High
Hazard" Sprinkler protection. The tenant needs to store almost 20,000 cubic
feet.

Does anyone have expertise in this area?
Thanks,
Greg


--
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments
/20120810/f3e9c5a0/attachment.html
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to