All:

I think Chris' comments are well thought out. 

I would not say "this is what the fire dept. will do". There are too many out 
there, and over the decades that a system is I/S practice may change. I would 
say it is much more likely that if FF's will be operating hose lines supplied 
by a pump that an engine will be hooked up, ready to supply. The world changes 
pretty fast when your attack line goes limp. 

Yours,

Bruce

Sent from my Motorola ATRIX™ 4G on AT&T

-----Original message-----
From: "Cahill, Christopher" <[email protected]>
To: "[email protected]" <[email protected]>
Sent: Wed, Aug 15, 2012 16:35:54 GMT+00:00
Subject: RE: Fire Dept. pumping into a system that has an onsite fire pump


1. Assumption  - Manual stop (as in base NFPA 20)

It keeps running because it's manual shut down.  If it is stopped manually and 
reset to normal it will restart if the pressure drops below start.  But if you 
stop it with the controller disconnect and leave it off it will obviously never 
restart until the switch is returned to normal.


1. Assumption - Automatic stop and the pressure is above its start point

It would shut down or exactly the same thing as closing the system control 
valve of whatever is flowing.  It will restart if the pressure drops below 
start.


2. I don't see why.  About the only good it might do is so you know after the 
incident and all the flow is stopped the pump is probably still running.  But 
as you clear the fire alarm panel it will tell you the same thing or if remote 
the central station.   One might even argue it's a bad idea to put a sign up 
there is a fire pump.  Some FF might get 'smart' and skip the FDC thinking 
'fire pump has this, I don't need my truck' only to find out later while 
walking through the rubble mopping up hot spots days later the battery was in 
the maintenance guys boat and the pump never started.  Stretching a bit I'll 
acknowledge. 

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation & Facilities Group
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Owen Evans
Sent: Wednesday, August 15, 2012 10:58 AM
To: [email protected]
Subject: Fire Dept. pumping into a system that has an onsite fire pump

What is the sequence of events (what happens) when a fire engine pumps into a 
system that has an onsite fire pump that is already in operation.


1.       Does the pump shut down if the fire engine pumps a greater pressure 
than the pump? How does that happen? Will the pump restart if the fire engine 
stops pumping?

2.       Should there be signage at the FDC notifying fire dept. that a fire 
pump may be in operation?




Owen Evans


-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120815/f06f4037/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120815/f4645dfa/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to