I've consulted with Tigerflow in the past on projects requiring standalone
fire pump enclosures.  They ship worldwide and I'm sure they would accept a
phone call to discuss this if you do not have access to a mechanical
engineer (HVAC type) who does this routinely.

As others have noted the engine needs combustion air and the pump room may
require supplemental cooling (or heating).  Depending on how the room is
classified by the Mechanical code, a minimum ventilation rate could be
required as well.  Generally, if not considered "occupied", there would be
no ventilation requirement (see 2009 International Mechanical Code, 401.2)
but your jurisdiction's code may be amended in some way.  I suppose the size
of the room is not the controlling factor if the only requirement is for the
pump driver combustion air.  For supplemental cooling this would matter when
calculating heat loss/gain through the enclosure.

www.tigerflow.com

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of David Bitton
Sent: Thursday, August 23, 2012 6:28 PM
To: [email protected]
Subject: Ventilation for diesel driven fire pump room

Where I can find guidelines for determining the size of the ventilation
openings in a pump room containing a diesel-engine driven pump? I imagine
that the size would depend on the room size (volume) and the size of engine.


 

David Bitton, ing.

Quest Loss Control Services Inc.

Les services de prévention des sinistres Quest inc.

5100, rue de la Savane, bureau 200

Montréal, QC H4P 1T8

(514) 341-4545

www.questlosscontrol.com

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120823/efe19989/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to