Excellent code analysis/decision tree formation Duane. And I still think we
need to work hard to put this idea of code versus standard, where the one
trumps the other because of a word in the title, even when the one given
the greater weight references the other as part of itself. I once had an
AHJ tell me there was no such thing as limited combustibility because some
unrelated chapter in IBC only mentioned non-combustibility so that the
silence in that section on limited combustibility trumped the rules in 13
(and 13 was an adopted reference) because 13 was "only a standard." This is
the kind of stuff I have bad dreams about. And Curtis, funny comment, but
often analysis of the simplest thing provides a platform for clearly seeing
much larger issues. I'm not saying this closet issue is a big deal
but Galileo gazed at the heavens with his "looking tube" and saw four moons
orbiting Jupiter. The direct result was Copernicus, Kepler, Newton and a
totally new world.

On Fri, Oct 5, 2012 at 6:54 AM, Curtis Tower <
cur...@centralfireprotection.net> wrote:

> I don't think anyone could ever foresee just how much discussion could be
> generated from a space barely large enough to store a vacuum cleaner
> in...[chuckles under breath].
>
> ----- Original Message ----- From: "Johnson, Duane (NIH/OD/ORS) [C]" <
> johnson...@mail.nih.gov>
> To: <sprinklerforum@firesprinkler.**org <sprinklerforum@firesprinkler.org>
> >
> Sent: Friday, October 05, 2012 8:24 AM
> Subject: RE: Stupid closet question...
>
>
>
> Based on NFPA 13, 2010 edition and NFPA 101, 2009 edition.
>
> Annex D is not part of the enforceable section of NFPA 13, unless a
> jurisdiction specifically adopts it (see section heading). In this case,
> Annex D is copied from NFPA 101, so if a jurisdiction adopts NFPA 101, it
> is enforceable from that perspective, but I would go do NFPA 101 directly,
> not Annex D of NFPA 13.
>
> As for the differences in requirements, per NFPA 101:1.2 the purpose of
> this code is to provide safety to life from fire while NFPA 13:1.2 has a
> purpose to provide a reasonable degree of protection for life and property.
> The two codes have slightly different purposes, hence they may have
> different design requirements for sprinklers. The committee agreed in the
> 2009 ROP to move NFPA 101 requirements to the Annex (see proposal 13-444).
>
> More importantly, the paragraphs you mention are for different
> occupancies. The exception from NFPA 13:8.15.8.2 to eliminate sprinklers in
> closets not exceeding 24 sq. ft. is for Hotels and Motels only. The
> exception from Annex D or NFPA 101:30.3.5.4 to exclude sprinklers in
> closets 12 sq. ft. or less is for New Apartments only. Interestingly, NFPA
> 101:31.3.5.4 permits the exclusion of sprinklers in closets not exceeding
> 24 sq. ft. for Existing Apartments. So, in reality, the NFPA 13 and Annex D
> references you cited do not contradict because they are for different
> occupancies. However, if you look at NFPA 101:29.3.5.5, Existing hotels and
> Dorms have the exception to exclude sprinklers in closets not exceeding 24
> sq. ft. But this is for Existing Hotels and Dorms only, there is not an
> exception in NFPA 101 for New Hotels and Dorms. This is arguably a
> difference from NFPA 13 to NFPA 101.
>
> Duane Johnson, PE
> Program Manager
> Division of the Fire Marshal (Support Contractor)
> Office of Research Services
> National Institutes of Health
> 301-496-0487
>
> "Protecting Science - One Sprinkler at a Time"
>
>
> -----Original Message-----
> From: Curtis Tower 
> [mailto:curtis@**centralfireprotection.net<cur...@centralfireprotection.net>
> ]
> Sent: Monday, October 01, 2012 2:49 PM
> To: sprinklerforum@firesprinkler.**org <sprinklerforum@firesprinkler.org>
> Subject: Re: Stupid closet question...
>
> Of course, I was only speaking of "adopted" codes.  I'm not familiar with
> all of the various code sets available for a jurisdiction to consider;
> however, the prevalent code set in Texas is IFC.  IFC references NFPA 13
> and
> 13R specifically for its installation requirements.  What I was ultimately
> alluding to was that if a jurisdiction had adopted NFPA 101, then it
> appeared that closets < 12s.f. could be omitted.  This question came up
> from
> a chapter contained in NFPA 2007, Special Occupancy Requirements, Section
> 21.20.13.2.1.  At the end of the sub-section NFPA 101, 30.3.5.4 was
> bracketed.  It is my understanding that a fair amount within that chapter
> was erroneously included in the 2007 standard.  Fast forward to the 2010
> Edition, and it was moved to a new Annex D.  I think this was to try to
> alleviate any confusion on what was required.  Annex D was titled Sprinkler
> System Information from the 2009 Edition of the Life Safety Code.  My
> understanding is that if the adopted code is anything other than NFPA 101,
> then the exceptions and omissions stated withing Annex D may and probably
> do
> not apply.  Of course, I'm always open to debate.
>
> Curtis
>
>
> ----- Original Message ----- From: "Ron Greenman" <rongreen...@gmail.com>
> To: <sprinklerforum@firesprinkler.**org <sprinklerforum@firesprinkler.org>
> >
> Sent: Thursday, September 27, 2012 6:26 PM
> Subject: Re: Stupid closet question...
>
>
> This is the conventional wisdom Curtis but I disagree. All model codes and
> standards are simply books until adopted, no matter what they are called.
> I'll use Washington as an example: The Revised Code of Washington (RCW)
> stipulates there will be a building code. The Building Code itself derives
> from the International Building Code (currently the 2009 edition) and all
> the references and amendments as proposed by the State Building Code
> Council as submitted to the governor and adopted by the legislature. In its
> final form it is called the Washington Administrative Code (WAC) Chapter
> 51-50, although we'll refer to it as the IBC in conversation. In the end
> though, before adoption it has no power of enforcement and after after
> adoption a referenced standard is a part of the WAC. So when chapter 9 of
> IBC references NFPA 13 and is adopted that way then NFPA 13 is a very long
> part of WAC 51-50, not some child of a lesser god. Had the legislature
> decided to not adopt the chapter 9 reference to NFPA 13 in IBC, but instead
> had replaced it with Hop On Pop or Cat In the Hat then that would be the
> sprinkler rules and criterion within 51-50. That a "code" tells you when
> and a "standard" tells you how is essentially a correct statement that only
> applies as separate and hierarchical as long as they are co-joined as one
> thing under the Law. Once adopted chapter 9, section X (I forget the number
> off-hand) is the code and, if sprinklers are required per Chapters 3 & 6,
> contains the how rules for installation. NFPA 101 unadopted is merely a
> very boring book and has no force of law no matter what the title may say
> about code, standard, what have you.
>
>
> On Thu, Sep 27, 2012 at 2:13 PM, Curtis Tower <
> curtis@centralfireprotection.**net <cur...@centralfireprotection.net>>
> wrote:
>
>  I believe that the root of the confusion stems from semantics.  NFPA 101
>> is referred to as a code, where NFPA 13, 13R, etc., is referred to as a
>> standard.  Many times, I have heard those of us in the business use the
>> term 'code' interchangeably with the term 'standard'.  This is technically
>> incorrect.
>>
>> Gov't entities have a plethora of code sets to choose from when deciding
>> what to adopt.  Most incorporated cities in Texas have adopted one version
>> or another of IFC, most with local amendments.  Tarrant County, which
>> oversees the unincorporated sections surrounding the Fort Wort area, has
>> adopted NFPA 101.
>>
>> To simplify things a bit...
>>
>> Code says WHAT gets sprinklered.
>>
>> The Standard says HOW.
>>
>> Example:  NFPA 13R does not require balconies to be sprinklered; however,
>> if the adopted code is IFC 2006, for example, then the balconies will be
>> sprinklered.
>>
>> In summation, your honor.
>>
>> If a jurisdiction has adopted NFPA 101, then it appears that the 12 s.f.
>> closet can be omitted.  By most other codes that I'm aware of, under NFPA
>> 13, the closets will be sprinklered regardless of size, with the exception
>> of hotels and motels under the stated criteria.
>>
>>
>>
>> ----- Original Message ----- From: "C&H Fire - Mike Gallello" <
>> mgalle...@chfireinc.com>
>> To: <sprinklerforum@firesprinkler.****org <sprinklerforum@firesprinkler.*
>> *org <sprinklerforum@firesprinkler.org>>
>> >
>> Sent: Wednesday, September 26, 2012 3:25 PM
>> Subject: Stupid closet question...
>>
>>
>> It's likely been asked before, but I don't recall - so please excuse my
>> possible ignorance!
>>
>> NFPA 13, 2010 - 8.15.8.2 Dwelling units, closets - hotels and motels
>> they can be deleted, conditionally regarding the 24sf and 3ft rule.
>>
>> Annex D (Pulled from NFPA 101) in two separate areas (D1.1.6.1 &
>> D2.19.2.1) states that closets under 12sf in dwelling units shall not be
>> required to be sprinklered.  The referenced 101 code is stated there as
>> well...
>>
>> I'm looking at it that the paragraphs of 101 referencing closets under
>> 12sf in dwelling units permits the omitting of sprinklers within these
>> closets.  (Not any with equipment of course).  There are some others
>> here that disagree, stating that since 13 addresses it, 101 isn't
>> applicable and that heads are required in the closets period.
>>
>> Anyone else have this kind of throw down in your offices?
>>
>>
>>
>> ______________________________****_________________
>> Sprinklerforum mailing list
>> Sprinklerforum@firesprinkler.****org 
>> <Sprinklerforum@firesprinkler.**org<Sprinklerforum@firesprinkler.org>
>> >
>> http://fireball.firesprinkler.****org/mailman/listinfo/****
>> sprinklerforum<http://**fireball.firesprinkler.org/**mailman/listinfo/**
>> sprinklerforum<http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum>
>> >
>>
>>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
>
> rgreen...@bates.ctc.edu
>
> http://www.bates.ctc.edu/**fireprotection/<http://www.bates.ctc.edu/fireprotection/>
>
> 253.680.7346
> 253.576.9700 (cell)
>
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>
> They are happy men whose natures sort with their vocations. -Francis Bacon,
> essayist, philosopher, and statesman (1561-1626)
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL:
> <http://fireball.**firesprinkler.org/mailman/**private/sprinklerforum/**
> attachments/20120927/a28e453c/**attachment.html<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120927/a28e453c/attachment.html>
> >
>
>
> ______________________________**_________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.**org <Sprinklerforum@firesprinkler.org>
> http://fireball.firesprinkler.**org/mailman/listinfo/**sprinklerforum<http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum>
>
>
> ______________________________**_________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.**org <Sprinklerforum@firesprinkler.org>
> http://fireball.firesprinkler.**org/mailman/listinfo/**sprinklerforum<http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum>
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

rgreen...@bates.ctc.edu

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121005/ee860da9/attachment.html>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to