NFPA 13:8.15.1.2 (2010 edition) states that "Concealed spaces of noncombustible 
and limited-combustible construction with limited access and not permitting 
occupancy or storage of combustibles shall not require sprinkler protection."  
Consider a masonry building with a metal roof deck, but the deck is sprayed 
with a foam material that functions as an air barrier.  The spray foam is 
exposed to view and doesn't meet the definition of limited-combustible at NFPA 
13:3.3.13 because the potential heat value is greater than 3500 Btu/lb.

The construction itself is noncombustible, but the surface exposed to view is 
combustible.  I'm pretty comfortable that the intent of NFPA 13 is that this 
space would need to be sprinklered, but would welcome either concurrence with 
that thought or an explanation of where I've gone astray. The answer to this 
potentially drives whether or not a fire pump is required and obviously has 
cost implications.  Thanks in advance for any opinions.  Sincerely,

Christopher H. Born, P.E.