The section in UFC 3-600-01 says "Galvanized piping is not permitted to be used 
in dry pipe, preaction, or wet pipe sprinkler systems."  It does not restrict 
the use in pumps or undergrounds where required IMO.  

I thought you were a contractor.  So I find it very hard to believe you have 
something to work up that has been 1391'd, designed and issued for bid or 
construction since last Friday.  What I'm getting at is you are probably still 
working under the old 3-600-01.  I suppose in theory if you are an engineer and 
a new project just hit your desk it could be applicable.  But then again I'd go 
back to the charging documentation like a 1391 and unless it was issued last 
Friday you would not have to use the '13 edition.  

We've been looking it over quick and, wow, there seems to be more questions 
than answers.  Sched 5 appears to be allowed.  Black dry systems w/o nitrogen.  
30% increase over 10% slope not 16%. Design are now per FM 3-26.  

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation & Facilities Group
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Justin Reid
Sent: Monday, February 04, 2013 7:47 AM
To: [email protected]
Subject: Internally Painted Pipe

I was just going through NFPA 20 2010 edition and noticed Section
4.13.1.2 talking about using galvanized steel pipe or steel pipe painted on the 
inside for suction piping in corrosive water conditions.

Anybody have any experience with pipe painted on the inside? A couple of 
internet searches later I have been unsuccessful in finding info about 
internally painted sprinkler pipe.

An updated UFC 3-600-01 was issued last week and galvanized piping is no longer 
permitted on DOD projects.

Justin Reid
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to