Black, cut grooved or thread, and nitrogen seem to be the best state of the art 
these days.  UFC was rumored to be going this route but only preaction seem to 
use preaction.  This galvanized issue is only applicable to military work.  
Carry-on as usual for private sector. 

To answer your question to what changed, in general MIC, thinwall, roll 
grooves, riser mount/tank-less compressors or bad installations all forced a 
closer look at the higher failure rates of dry system piping.  Use thinwall 
pipe roll grooved with a riser mount compressor and don't slope correctly and 
you get a quick rusting out problem.  That combination seems to be popular 
going back a few years and beyond.  

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation & Facilities Group
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN





-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ford, Charles
Sent: Monday, February 04, 2013 10:21 AM
To: [email protected]
Subject: RE: Internally Painted Pipe

Please excuse my ignorance, but I thought galvanized pipe was the preferred 
material for all types of dry pipe sprinkler systems. Thought FM required it.
What changed? MIC?

C. Burton Ford
NICET Certified IV
NFPA Certified Fire Protection Specialist Cintas Fire Protection Inc
1038 Conshohocken Rd
Conshohocken, PA 19428
Tel 610-233-1400
Fax 610-233-1401


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Cahill, 
Christopher
Sent: Monday, February 04, 2013 11:04 AM
To: [email protected]
Subject: RE: Internally Painted Pipe

The section in UFC 3-600-01 says "Galvanized piping is not permitted to be used 
in dry pipe, preaction, or wet pipe sprinkler systems."  It does not restrict 
the use in pumps or undergrounds where required IMO.

I thought you were a contractor.  So I find it very hard to believe you have 
something to work up that has been 1391'd, designed and issued for bid or 
construction since last Friday.  What I'm getting at is you are probably still 
working under the old 3-600-01.  I suppose in theory if you are an engineer and 
a new project just hit your desk it could be applicable.  But then again I'd go 
back to the charging documentation like a 1391 and unless it was issued last 
Friday you would not have to use the '13 edition.

We've been looking it over quick and, wow, there seems to be more questions 
than answers.  Sched 5 appears to be allowed.  Black dry systems w/o nitrogen.  
30% increase over 10% slope not 16%. Design are now per FM 3-26.

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation & Facilities Group Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For *Registered in: MN




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Justin Reid
Sent: Monday, February 04, 2013 7:47 AM
To: [email protected]
Subject: Internally Painted Pipe

I was just going through NFPA 20 2010 edition and noticed Section
4.13.1.2 talking about using galvanized steel pipe or steel pipe painted on the 
inside for suction piping in corrosive water conditions.

Anybody have any experience with pipe painted on the inside? A couple of 
internet searches later I have been unsuccessful in finding info about 
internally painted sprinkler pipe.

An updated UFC 3-600-01 was issued last week and galvanized piping is no longer 
permitted on DOD projects.

Justin Reid
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

This e-mail transmission contains information that is intended to be 
confidential and privileged. If you receive this e-mail and you are not a named 
addressee you are hereby notified that you are not authorized to read, print, 
retain, copy or disseminate this communication without the consent of the 
sender and that doing so is prohibited and may be unlawful. Please reply to the 
message immediately by informing the sender that the message was misdirected. 
After replying, please delete and otherwise erase it and any attachments from 
your computer system. Your assistance in correcting this error is appreciated.


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to