Steve,

I think the following is where I went wrong with the previous post. 

13R - 6.9.1 Sprinklers shall be installed in all areas except where omission is 
permitted by 6.9.2 - 6.9.7. 

Thanks,

Rod


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Rod DiBona
Sent: Wednesday, February 13, 2013 8:34 AM
To: [email protected]
Cc: Brent Zimiga
Subject: RE: Exterior closets....again but different

Steve,

Thank you for your response. I do agree that the contested closets are outside 
the dwelling unit. I am looking but haven't found where 13R says that areas 
outside the dwelling unit shall be PROTECTED by 13. I see 6.8.2.1 that says 
"For areas outside the dwelling unit, the design discharge and design area 
criteria shall comply with NFPA 13"....No mention of coverage?... For example, 
we don't sprinkler concealed combustible and attics in 13R which are outside 
the dwelling unit. So this is the heart of the issue does chapter 8 of 13 
apply? Is so where does 13R state that it does apply for protection of areas? 
If it does apply, then the 13R exemptions for other areas outside the dwelling 
unit trump 13 requirements? Not trying to be difficult and this is not a big 
add to the project but truly want to come to an understanding on this one. 
Wonder why the closets on the decks would be exempted but not a breezeway? 
Egress? Thanks!

Rod at Rapid 

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: Tuesday, February 12, 2013 10:52 PM
To: [email protected]
Subject: RE: Exterior closets....again but different

I agree with the AHJ.   Exception to closets on exterior balconies presumes 
they are within (or directly communicating with) dwelling unit.  If you agree 
that the contested closets are outside of the dwelling unit, where is the 
exception in 13 that would not require sprinklers in these compartments?  
Methinks you're trying to split hairs with the "design criteria" intent 
argument - what do you mean by that, exactly?   If hydraulics, then the answer 
is yes, but 13R also states that areas outside the dwelling unit shall be 
protected per 13, so I think that Chapter 8 of 13 applies, period.   

The foregoing is my opinion only, and does not necessarily represent the 
opinion or intent of the Technical Committee on Residential Sprinkler Systems.

Steve L.


-----Original Message-----
From: [email protected] on behalf of Rod DiBona  
Sent: Tue 2/12/2013 4:25 PM
To: [email protected]
Subject: Exterior closets....again but different
 
NFPA 13R 2007- New apartment building with a breezeway on the bottom level that 
is enclosed and protected with dry sidewalls. 2 closets (one plumbing and the 
other electrical data) in that breezeway that only open to the breezeway. No 
fuel fired equipment. No heating or air conditioning equipment. Had it in my 
mind that these closets would not have to be sprinklered. Fire marshal is 
disagreeing. After review I am not so sure. Seems like the intent is to not 
require protection but by the letter I can't quite get there. Am I missing 
something?

2007 NFPA 13R 6.9.6 - "Sprinklers shall not be required in............(last 
sentence) ... "and other concealed spaces that are not intended for living 
purposes or storage and do not contain fuel fired equipment." -   He pointed 
out that a closet is not a concealed space...... Ok then.....

2007 NFPA 13R 6.9.7 " Sprinklers shall not be required in closets on exterior 
balconies, regardless of size, as long as there are no doors or unprotected 
penetrations from the closet directly into the dwelling unit. - His point is 
that these closets are not on exterior balconies....

He says that it is outside the dwelling unit and therefore protected by NFPA 
13. My comment is that I believe 2007 NFPA 13R only requires the "design 
criteria" of 13 to be followed for areas outside the dwelling unit.  Clarified 
in section A.6.8.2.

He says show me in 13R where you can exclude.....


Thoughts?


[Description: LOGO_10]
Rod DiBona
Vice President
Rapid Fire Protection
office : (605)348-2342
fax : (605)348-0108
cell : (605)391-3553
www.rapidfireinc.com<http://www.rapidfireinc.com>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20130213/ae9e854f/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 6561 bytes
Desc: image001.jpg
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20130213/ae9e854f/attachment.jpg>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-------------- next part --------------
A non-text attachment was scrubbed...
Name: winmail.dat
Type: application/ms-tnef
Size: 4240 bytes
Desc: not available
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20130212/786c66f1/attachment.bin>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to