This is a great opportunity to remind all forum subscribers that
proposals are being accepted for the 2015 cycle of the 13's; ROP closing
date is 5/31/13.   As one of AFSA's reps on the Residential TC, I would
encourage everyone who has energy about the standard to submit a
proposal if you believe that there is an aspect that warrants revision
or, as in the case of this issue, where there may be confusion about
intent of the standard.   The TC's may summarily reject proposals that
aren't well-substantiated or written in a conforming manner, so if you
would like to submit one but feel the need to discuss how to compose or
submit it, feel free to email me off-forum, or contact Roland at HQ.

Steve 




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Rod
DiBona
Sent: Wednesday, February 13, 2013 8:19 AM
To: [email protected]
Subject: RE: Exterior closets....again but different

Steve,

I think the following is where I went wrong with the previous post. 

13R - 6.9.1 Sprinklers shall be installed in all areas except where
omission is permitted by 6.9.2 - 6.9.7. 

Thanks,

Rod


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Rod
DiBona
Sent: Wednesday, February 13, 2013 8:34 AM
To: [email protected]
Cc: Brent Zimiga
Subject: RE: Exterior closets....again but different

Steve,

Thank you for your response. I do agree that the contested closets are
outside the dwelling unit. I am looking but haven't found where 13R says
that areas outside the dwelling unit shall be PROTECTED by 13. I see
6.8.2.1 that says "For areas outside the dwelling unit, the design
discharge and design area criteria shall comply with NFPA 13"....No
mention of coverage?... For example, we don't sprinkler concealed
combustible and attics in 13R which are outside the dwelling unit. So
this is the heart of the issue does chapter 8 of 13 apply? Is so where
does 13R state that it does apply for protection of areas? If it does
apply, then the 13R exemptions for other areas outside the dwelling unit
trump 13 requirements? Not trying to be difficult and this is not a big
add to the project but truly want to come to an understanding on this
one. Wonder why the closets on the decks would be exempted but not a
breezeway? Egress? Thanks!

Rod at Rapid 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve
Leyton
Sent: Tuesday, February 12, 2013 10:52 PM
To: [email protected]
Subject: RE: Exterior closets....again but different

I agree with the AHJ.   Exception to closets on exterior balconies
presumes they are within (or directly communicating with) dwelling unit.
If you agree that the contested closets are outside of the dwelling
unit, where is the exception in 13 that would not require sprinklers in
these compartments?  Methinks you're trying to split hairs with the
"design criteria" intent argument - what do you mean by that, exactly?
If hydraulics, then the answer is yes, but 13R also states that areas
outside the dwelling unit shall be protected per 13, so I think that
Chapter 8 of 13 applies, period.   

The foregoing is my opinion only, and does not necessarily represent the
opinion or intent of the Technical Committee on Residential Sprinkler
Systems.

Steve L.


-----Original Message-----
From: [email protected] on behalf of Rod DiBona  
Sent: Tue 2/12/2013 4:25 PM
To: [email protected]
Subject: Exterior closets....again but different
 
NFPA 13R 2007- New apartment building with a breezeway on the bottom
level that is enclosed and protected with dry sidewalls. 2 closets (one
plumbing and the other electrical data) in that breezeway that only open
to the breezeway. No fuel fired equipment. No heating or air
conditioning equipment. Had it in my mind that these closets would not
have to be sprinklered. Fire marshal is disagreeing. After review I am
not so sure. Seems like the intent is to not require protection but by
the letter I can't quite get there. Am I missing something?

2007 NFPA 13R 6.9.6 - "Sprinklers shall not be required
in............(last sentence) ... "and other concealed spaces that are
not intended for living purposes or storage and do not contain fuel
fired equipment." -   He pointed out that a closet is not a concealed
space...... Ok then.....

2007 NFPA 13R 6.9.7 " Sprinklers shall not be required in closets on
exterior balconies, regardless of size, as long as there are no doors or
unprotected penetrations from the closet directly into the dwelling
unit. - His point is that these closets are not on exterior
balconies....

He says that it is outside the dwelling unit and therefore protected by
NFPA 13. My comment is that I believe 2007 NFPA 13R only requires the
"design criteria" of 13 to be followed for areas outside the dwelling
unit.  Clarified in section A.6.8.2.

He says show me in 13R where you can exclude.....


Thoughts?


[Description: LOGO_10]
Rod DiBona
Vice President
Rapid Fire Protection
office : (605)348-2342
fax : (605)348-0108
cell : (605)391-3553
www.rapidfireinc.com<http://www.rapidfireinc.com>

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20130213/ae9e854f/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 6561 bytes
Desc: image001.jpg
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20130213/ae9e854f/attachment.jpg>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-------------- next part --------------
A non-text attachment was scrubbed...
Name: winmail.dat
Type: application/ms-tnef
Size: 4240 bytes
Desc: not available
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20130212/786c66f1/attachment.bin>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to