The predominate driving factor for the areas listed in 6.6.6 is that they are outside the heated envelope. Other areas are clumped in there too like concealed spaces but the community of the majority is temperature. Just like 6.6.5 where the outside corridor open on both ends can run through the middle of the building enclosed on all sides except for the open ends. Even the balcony closet - typically not heated. The garage is the big exception but that's understandably.
Roland garages are addressed separately On Feb 13, 2013, at 7:34 AM, Rod DiBona <[email protected]> wrote: > Steve, > > Thank you for your response. I do agree that the contested closets are > outside the dwelling unit. I am looking but haven't found where 13R says that > areas outside the dwelling unit shall be PROTECTED by 13. I see 6.8.2.1 that > says "For areas outside the dwelling unit, the design discharge and design > area criteria shall comply with NFPA 13"....No mention of coverage?... For > example, we don't sprinkler concealed combustible and attics in 13R which are > outside the dwelling unit. So this is the heart of the issue does chapter 8 > of 13 apply? Is so where does 13R state that it does apply for protection of > areas? If it does apply, then the 13R exemptions for other areas outside the > dwelling unit trump 13 requirements? Not trying to be difficult and this is > not a big add to the project but truly want to come to an understanding on > this one. Wonder why the closets on the decks would be exempted but not a > breezeway? Egress? Thanks! > > Rod at Rapid -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20130215/730b26e4/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum