It's in IBC 507.3.

2.      The automatic sprinkler system shall not be required in areas occupied 
for indoor participant sports, such as tennis, skating, swimming and equestrian 
activities in occupancies in Group A-4, provided that:

2.1.    Exit doors directly to the outside are provided for occupants of the 
participant sports areas; and

2.2.    The building is equipped with a fire alarm system with manual fire 
alarm boxes installed in accordance with Section 907.

And most racquetball courts are A-3 anyway unless you have defined spectator 
seating, which I haven't seen personally.  A viewing deck above or glass wall 
IMHO isn't the same.   So this A-4 exception may not help you. Also, in the 
commentary it makes the point A-4 exception only applies when in unlimited area 
buildings so you just have to watch what the mixed uses are.  This goes to 
Steve's comment about separation of occupancies.  If you are unlimited and fit 
within the definitions of unlimited I'm seeing it as you can not sprinkler the 
A-4 and still be unseperated.  No direct show stoppers as these are typically 
in A-3's and they can be unlimited when one story.  Got a two story health club 
and you start to run into issues even if you somehow get to the A-4 occupancy 
in the first place.  

Don't get me wrong there are many places I think sprinklers are kinda silly.  
The above though is Code and I don't like to override with common sense too 
often.   I have too good a life to waste on an outlier event.  

BTW, I've played off and on.  Been a number of years, but I don't recall 
hitting the ceiling ever never mind often enough or hard enough to 
statistically hit too many heads.   Am I miss-remembering? 

As far as other solution not previously discussed are there areas of the 
ceiling less likely to get hit?  Re-space and get closer to the corners? Also, 
at what rate are they getting knocked off.  A few times a  year, buy a ladder, 
few times a day yeah I see the issue.  

You still have the exception of  IFC 903 1.1.1.1 
4.      Rooms or areas that are of noncombustible construction with wholly 
noncombustible contents.

But I'd think the requirement for detection would just swap the details of the 
same problem.  

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation & Facilities Group
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN





-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Thursday, March 21, 2013 5:50 PM
To: [email protected]
Subject: Re: Racquet Ball Court

2003 IFC 903.2.1.4 Group A-4.
An automatic sprinkler system shall be provided for Group A-4 occupancies where 
one or more of the following conditions exists:  
1.
2.
3.

Exception: Areas used exclusively as participant sports areas where the main 
floor area is located at the same level as the level of the exit discharge of 
the main entrance and exit. 

This exception has been deleted from all later versions on the code. 