Brad,

No, thank you for the offer on the spreadsheet, I have myown, and thanks to some very patient structural engineers on the hanging and bracing committee, and the Eighth Edition of the Manual of Steel Construction, I have all the formulas I could ever need or use. And, because I felt so unprepared at the first ROP meeting I attended in 2008, I spent that summer annoying those same structural engineers to help me understand those formulas, what they meant, and how to interpret them for the work I do relative to fire sprinkler systems. Even thoughI think I have a fairly complete understanding of the formulas, and their results, I would never dream of giving someone those formulas and sending them out on their own to use them correctly. I'm not a structural engineer, and I don't pretend to be one.

Yes, you did hit a nerve for me, in that that the explanation contained a significant error, and anyone taking that guidance as factual was going to get out on a limb where they would be in serious trouble. Perhaps to the point of failure of the trapeze to hold the load, despite the safety factors built in (5x weight, 250#, 15,000 instead of 30,000), and all because they followed the path you described.

I do completely understand your need to understand the things in a code or standard, and I applaud that, and encourage that. The danger in that is when you, or me, or anyone elsefor that matter, describes that understanding to others without first checking the language and documentation to make sure there was no significant error or omission, because others may be tempted to act on that information. An example is the reference to half the weight and half the length, neither of which are even remotely applicable. Errors of that nature get people sued, or worse.

The tables are in NFPA 13 for a reason, and to me that reason has been so that I can do my work in designing systems without being a registered engineer with experience in any of the myriad of topics covered by tables in that document. For example, in the last cycle, the trapeze tables were proposed to be extended tocover spans up to 20' in length, in 6" increments. The substantiation for that included the following text: "For spans more than 20 feet. the trapeze should be looked at further by an expert as many scenarios would then involve a joint in the trapeze which could create the need for additional analysis."

The committee accepted that proposal, in principle, however it limited the table to 16', and provided the following change: 2) Add annex material as follows: A.9.1.1.6.1(a)The table values are based on the trapeze being a single continuous member." In support of that statement, the committee wrote: "The TC feels that for spans in excess of 16 feet, the values should be reviewed on a case by case basis."

In what you wrote, I took it to encourage any reader to simply double the section modulus required for a 9'-0" span, and that was good enough. That's contrary to the intent of the committee, and the published information on how that table was developed.

The above is myopinion only, and does not reflect that of the committee on hanging and bracing of NFPA 13.
*

PARSLEY CONSULTING

*

Ken Wagoner

760.745.6181 voice

760.745.0537 fax

website: www.ParsleyConsulting.com <http://www.ParsleyConsulting.com>

On 6/3/2013 9:48 AM, Brad Casterline wrote:
Ken,

Sorry if I touched a nerve or upset you. I am nothing but a designer with a
trust issue; I simply do not trust anything in any code or standard until I
can explain it to myself like I'm 6 years old.

May I send you a spread sheet I made many years ago? It will allow you to
quickly calc the req. sec. mod. based on any pipe type (not just S10 or
S40), any span, any length of pipe being hung, no matter 'where in the span'
you are. It calculates the amount of steel based on 490 lbs/ft3 and water at
62.4 lbs/ft3. It also calculates the Available Section Modulus for pipe
trapeze based on type (i.e. not just s10 or s40). You will see it matches
the table perfetctly.

If you still say Gibberish I will print this post and eat it :)

ps, the spreadsheet is rather ugly and not real user friendly because it
takes after me


On 6/3/2013 7:51 AM, ParsleyConsulting wrote:
Brad,
     Part 1 - Gibberish.  Pure and simple.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to