It shouldn't be a problem if the demand gpm is at or below the actual 50% test 
point. I assume you have an actual pump test? The only thing lacking would be a 
water supply safety factor if required by contract or AHJ.

Ron F

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Monday, July 08, 2013 8:44 AM
To: [email protected]
Subject: Using points on the pump curve for calculations

Got a calculation I'm reviewing where the designer used the fire pump 50% test 
point for his calculations and plugged it in as the City water supply info.   
The water source for the fire pump is an aboveground suction tank.

I've not done this and was always taught that when a fire pump was used you 
used the fire pump churn, rated and 150% values in the calculation for your 
water source.  

Any thoughts, did I miss a memo on a new or other way to calc when using a fire 
pump?

Craig L. Prahl, CET   