Yes the demand represents approximately 40% of the pump rating so it is below 
the 50% test point.  Yes we have an actual pump test.

Any safety factor based on actual available versus demand is SO not an issue 
based on this system.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Monday, July 08, 2013 12:04 PM
To: [email protected]
Subject: RE: Using points on the pump curve for calculations

It shouldn't be a problem if the demand gpm is at or below the actual 50% test 
point. I assume you have an actual pump test? The only thing lacking would be a 
water supply safety factor if required by contract or AHJ.

Ron F

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Monday, July 08, 2013 8:44 AM
To: [email protected]
Subject: Using points on the pump curve for calculations

Got a calculation I'm reviewing where the designer used the fire pump 50% test 
point for his calculations and plugged it in as the City water supply info.   
The water source for the fire pump is an aboveground suction tank.

I've not done this and was always taught that when a fire pump was used you 
used the fire pump churn, rated and 150% values in the calculation for your 
water source.  

Any thoughts, did I miss a memo on a new or other way to calc when using a fire 
pump?

Craig L. Prahl, CET   
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to