It was my understanding that this section was addressing ductile iron pipe 
since there was some confusion on whether you should be using Sch 40 or Sch 10 
carbon steel once above the slab or if it was acceptable to extend the ductile 
iron pipe above the slab.

Plastic above the slab is a disaster waiting to happen.  I've seen pictures of 
plastic stub-ups melting in a fire scenario and rendering the sprinkler system 
inoperable.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Roland 
Huggins
Sent: Wednesday, July 10, 2013 10:58 AM
To: [email protected]
Subject: Re: Underground Stub-Up

Historically I've always said NO since a pure application of the listing would 
conflict with having underground pipe installed above ground. But a pure 
application of terms doesn't necessarily get in the way of actions taken by the 
technical committee.  The same could be said for requiring listed back flow 
preventers since they are classified (an unacceptable category for all other 
listed devices).  Since this is a common practice, the TC addressed stub-ups 
last cycle by adding the below:
6.3.1.1.1* Underground pipe shall be permitted to extend into the building 
through the slab or wall not more than 24 in. (0.6 m). 

Roland

Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Jul 10, 2013, at 5:38 AM, Mike Hairfield <[email protected]> wrote:

> Got a project that HDPE AWWA C906  pipe and fittings were installed.
> 
> 
> 
> The stub-up through the floor is a piece of HDPE AWWA C906 pipe with
> 
> a cap fused on the end and not rodded.
> 
> 
> 
> I've never seen this done before, is it acceptable with NFPA #24?
> 
> 
> 
> Mike Hairfield
>                                         
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to