You must mean south of the Canadian border...seen that here plenty of times. I 
don't know if it's any better or worse than weld, grooves or threads.  All have 
their shortcomings.  I have heard concerns about using them without cutting the 
hole, which models I can think of not possible.  And another concern is the 
disks or fines getting left in the pipe.  Of course this is an issue with 
welded outlets too.  And I suppose to a lesser extent threads and grooves.  

And for those that occasionally dabble in military they prohibit (in their 
code) in new but allow in existing for remodeling. 

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation & Facilities Group
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Friday, July 19, 2013 10:28 AM
To: [email protected]
Subject: RE: Mechanical Tees REPLY

South of the border I've seen entire systems installed with nothing but 
mechanical tees.  They didn't fabricate anything. 

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Matt Grise
Sent: Friday, July 19, 2013 11:04 AM
To: [email protected]
Subject: RE: Mechanical Tees REPLY

I have seen them prohibited under nfpa 13 6.4.6.1 because they are not a 
one-piece fitting (the saddle and also the strap). I did not agree with the 
interpretation, but that was the given reason.

Matt Grisé PE*, LEED AP, NICET II
Sales Engineer
Alliance Fire Protection
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO 

913.888.0647 ph
913.888.0618 f
913.927.0222 cell
www. AFPsprink.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Friday, July 19, 2013 9:50 AM
To: [email protected]
Subject: Re: Mechanical Tees REPLY

Ladies/Gentlemen:

As designers/specifiers (former fitter/installer), I see no reason to prohibit 
mechanical tees from (vitually) any commercial project. Our PE/FPE's do not 
restrict their use and, frankly, they can come in pretty handy at times. 
If anyone knows of an actual "Code"/NFPA-13 citation, I would sure love to hear 
it. That said - and engineering "judgement" acknowledged - if the project 
spec's prohibit MT's - then they cannot be used, in my opinion. They are used 
on our projects all the time. Also, our inspectors (retired State Fire
Marshals) have no 'grievances' against MT's.

"Roust-a-Bout" fittings - now that is a different matter. Are they still used??

Regards to all,

Jerry
[email protected]

Jerry D. Watts, SFPE
President & Co-Founder
ACCENT FIRE ENGINEERING INT'L. Ltd.*
Santa Fe, New Mexico USA
(800) 503.1961

*Licensed Fire Engineers - Architects/Inspectors/Fire Investigators:  AZ CA  CO 
 NM  NV  NY  TX  UT  KS  MD  MS _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to