Hello Craig,

Been done in North of the border in South Carolina also.

Friday, July 19, 2013, 11:28:18 AM, you wrote:

> South of the border I've seen entire systems installed with nothing
> but mechanical tees.  They didn't fabricate anything. 

> Craig L. Prahl, CET   
> Fire Protection 
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension  74102
> [email protected]



> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Matt 
> Grise
> Sent: Friday, July 19, 2013 11:04 AM
> To: [email protected]
> Subject: RE: Mechanical Tees REPLY

> I have seen them prohibited under nfpa 13 6.4.6.1 because they are
> not a one-piece fitting (the saddle and also the strap). I did not
> agree with the interpretation, but that was the given reason.

> Matt Grisé PE*, LEED AP, NICET II
> Sales Engineer
> Alliance Fire Protection
> 130 w 9th Ave.
> North Kansas City, MO 64116

> *Licensed in KS & MO 

> 913.888.0647 ph
> 913.888.0618 f
> 913.927.0222 cell
> www. AFPsprink.com 


> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of 
> [email protected]
> Sent: Friday, July 19, 2013 9:50 AM
> To: [email protected]
> Subject: Re: Mechanical Tees REPLY

> Ladies/Gentlemen:

> As designers/specifiers (former fitter/installer), I see no reason
> to prohibit mechanical tees from (vitually) any commercial project.
> Our PE/FPE's do not restrict their use and, frankly, they can come in pretty 
> handy at times.
> If anyone knows of an actual "Code"/NFPA-13 citation, I would sure
> love to hear it. That said - and engineering "judgement"
> acknowledged - if the project spec's prohibit MT's - then they
> cannot be used, in my opinion. They are used on our projects all the
> time. Also, our inspectors (retired State Fire
> Marshals) have no 'grievances' against MT's.

> "Roust-a-Bout" fittings - now that is a different matter. Are they still 
> used??

> Regards to all,

> Jerry
> [email protected]

> Jerry D. Watts, SFPE
> President & Co-Founder
> ACCENT FIRE ENGINEERING INT'L. Ltd.*
> Santa Fe, New Mexico USA
> (800) 503.1961

> *Licensed Fire Engineers - Architects/Inspectors/Fire
> Investigators:  AZ CA  CO  NM  NV  NY  TX  UT  KS  MD  MS
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


-- 
Best regards,
 Charles                            mailto:[email protected]